what is transformar load balancing ?
Answers were Sorted based on User's Feedback
Answer / monika khare
Billing program (for PUDs, cities, etc...) that will track transformers.
Part of that is a 'load balancing' report. The example of a 'load
balancing' report that I have gives actual usage (in KWH) of all the meters
connected to it, converted to KVA and the % it is of the maximum KVA rating
of the transformer. My question is - should I be concerned with the actual
usage or the potential usage? My guess is that if every meter reads the max
usage, it will overload 99% of their transformers. Is this typical in the
energy industry? Are the transformers usually balanced with the actual
usage or the potential usage?
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / priya
Let us consider a 11kv/433v 100KVA DTR; LV side current rating is 133.33A(100000/(1.732*433)). Now max loading on LV side is 133.33A in each phase. If loading on each phase is say 50A 50A 50A then load is said to be balanced. If loading is say 100A in Rphase 30A in Yphase and 20A in Bphase then the load is said to be unbalanced.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is static switch where it can be use?
how to carry out Magnetizing Current Test on Distribution transformer and what purpose we are doing this test.
What will be the size of cable required for 5.5 KW motor ( Full load current 10 Amps approx.), Starting current with DOL is 120 Amps. Aprrox. Short circuit current with LLLG fault is 2000 Amps Approx.
Why the capacitor are connected in Delta(Three Phase) for power factor improvement ?
which is better ac or dc?
how much loading in terms of ampere can put on 5 MVA,33/11 KV TRANSFORMER having rated current 263 Amp ?????????
why diesel tank is earthed
what can be the causes of capacitor start motor having a higher current that its actual
How can I communicate with an Areva MiCOM P121 relay by RS485 port? In other word, which command can I send and what information can I have recieved? please send some refrences, please. thanks
explain the functions of main isolation switches
Why we Do not connect the windings of the motor in delta? & what would happen if we do that? I mean the winding themselves not the three lines that are coming to the motor?
Explain how you decide what size of electrical wire do you need?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)