If a control valve is hunting means means if we are giving
50% to the cv, the cv will open at 51% then slowly slwoly
it will reaches 49% , then it will reaches again 50%, this
type of action occured frequntly.. so what to do for solve
this problem. The possible cause is in volume booster or
positioner's relay.. positioner is double acting .. and
make siemens..sipart.The cv is double acting and mounted
for anti surge operation, it having 4 nos. volume booster,
one sov, one positioner, etc..?
Answers were Sorted based on User's Feedback
Check the following items:
1. Any loose connection or leakage of pneumatic signal.
Check all tube fittings with soap solution.
2.Check the gland packing should not be so tight. If feel
tight, get loose them a bit.
3. Check the pneumatic relays of Postioner. Get clean its
ports, nozzle, flapper etc.
4. Also check, that linkage, feed back mechanical link
should not have any dent, grove, burs etc.
aftabmazari@yahoo.com
Is This Answer Correct ? | 17 Yes | 0 No |
Answer / avinash d. pagar
Also please check volume booster function separately with
out positioner and then set factory setting of positioner.
again calibrate positioner by auto calibration. mostly
hunting and over shooting issues cause by booster error.
Is This Answer Correct ? | 4 Yes | 0 No |
Instrumentation symbols interpration, P& ID, Logic diagram analysis, Electrical drawing analysis.
What is the difference between DCS and SCADA?
hw to calibration a control valve?
diff c and c++
what's the reson that,Load is not same on VFD I/P and O/P Side.whenever DOL condition load is same I/P and O/P side.
can we use flow transmitter instead of level transmitter?
How r the calculation of process line mpm.
0 Answers Bhushan Power Steel,
what is weighfeeder
Where should we terminate the shield and why?
How to calibrate the magnetic flow meter and how to correct the flow if it is showing more flow.
5 Answers Bohra Industries Limited, TCL,
Describe how to calibrate various types of instruments and transmitters using ISA industrial consensus standard techniques.
How would i calibrate a new commissioned flow transmitter???