WHY TEMPERATURE TRANSMITTER USED AS WE CAN CONTROL THROUGH THERMOCOUPLE/RTD
Answers were Sorted based on User's Feedback
Answer / lokesh gatty
We cannot control through thermocouple/RTD, they are only
measuring elements,which is connected to temperature
controller which as set value for which point it has to
control temperature (PID/Relay logic control)..Meanwhile
Temperature transemeter is used to convert mv/ohm to anolog
signal(4--20 ma)...we have to refer ohms/mv to degree Celsius
table
| Is This Answer Correct ? | 24 Yes | 1 No |
Answer / aditya kaushik
When we are using the rtd/thermocouple, The output is in mv
or Ohm variation wrt temperature, that will nt be directlyy
processed by our dcs/PLC so we are using transmitters to
convert it to 4-20 ma accordingly, bt now a days rtd cards
are available widely with plc vendors so we can now a days
use directy without transmitters also,\\thnx,
aditya
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / george mathews
Neither temperature transmitter not the thermocouple or Rtd
can control the process. Because as we know Thermocouple and
RTD are nothing but measuring medium , their only work is to
measure the temperature , and for the transmitter it nothing
but a transducer whose only work is to send the measurement
in d form of mA (4 to 20 mA.)
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / palanisamy
If you transmit Thermocouple/RTD signal for a longer
distance, it can easily pickup noise & you will not get a
steady reading in the receiving instrument. By providing a
temperature transmitter, we can avoid noise pickup.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / chandrakant kale
WE GENERALLY NEED TO CONTROL THE PROCESS PARAMETER
(TEMPERATURE) SO FOR THAT WE NEED TRANSDUCER.WHICH SEND 4-20
MA TO THE DEVICE WHICH IS TO BE CONTREOLLED. TC IS ONLY FOR
SENSING TEMP.
| Is This Answer Correct ? | 1 Yes | 4 No |
what is "smart" in smart transmitter ?
Witch type cable use for rtd ,why?
I have observed in field instrumentation work... I remove the fuse of an analog transmitter then it shows 7.75 kg/sq cm (which is practically wrong value)in DCS and when put the fuse it shows 0 in dcs. Then cheach the field transmitter termination and found moister. clean that and then it shows 1.1 kg/ sq cm which is right value. Please describe the above phenomenon.
sir ,iam in dem urgent need of HPCL Paper of Instrumentation Branch plz send me at your earliest convenience at ujjwal_sharma1983@yahoo.com
which type of zones used for boiler? & why ?
what is the difference between transmitter and converters?
how can calibrate vacume trasmitter by HART COMMUNICATOR ?
What is open loop and close loop?
4 Answers L&T, Pearl Distillery,
relation between flow and differential pressure.
what is proportional & what is proportional band
what is actual drum level and compensated drum level?
As you are fresher in Instrumentation & control engineer.Then why should I select you?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)