how to caluculate flow by using transmitter?tell me plz I am
eagerly waiting for your reply..
Answers were Sorted based on User's Feedback
Answer / ginoop
easiest formula to find Ma
of flow in square root
(sqrt of % x 16)/10 +4
eg : ma of 25%
sqrt of 25x 16/10+4
=5x16/10+4
=80/10+4
=8+4=12
ma of 25% flow in sqrt =12
eg : ma of 50%
sqrt of 50x 16/10+4
=7.07x16/10+4
=113.13/10+4
=11.31+4=15.31
ma of 50% flow in sqrt=15.31