Answer / pankaj nandasana
As you know....0.2 to 1 kg/cm2 is equal to 3-15 psig..
Generally we are considering this range...reasons are following...
1) Suppose if your have set lower limit at 0 psig, then how you can differentiate zero signal level and pipe breakage..!!!! You can not distinguish two thing..That why we select some elevated range from 0 psig.
2) Our all instrument are producing linear response in the range of 3-15 psig.
3) Pneumatic supply to all instrument is 20 psig..so alway there is bleading of air from instrument..for standardlisation purpose all are considering 3-15 psig..
| Is This Answer Correct ? | 33 Yes | 0 No |
Answer / ashish namdev, bina refinery [
The diaphragm design of all control valves are universal and
the out of the actuators are 3 to 15 psi.When more than the
15 psi pressure is acting to the diaphragm that will lead it
to faulty so we use the 0.2 to 1.0kg/cm2 for control valves.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / s k
because the control valve work within the specified pressure
range of about 0.2 to 1.0 kg/cm2.
| Is This Answer Correct ? | 2 Yes | 8 No |
Calibration of flow transmitter.
please tell me how to convert double acting ytc positioner yt-1200 into single acting ytc positioner ?
please send the sample qustion paper for iocl written test ..
What is difference between magnetic flow transmitter & Electromagnetic flow transmitter?
how to explain PID?
Which is your favourite subject & explain any one topic of it.
why use 50% lel methane gas concentration for gas detector calibration instead of 60% lel gas concentration whereas the hi alarm set at 60% lel.
What is basic of instrumentation
my data card only does run in my mobile so how can change it that it run other mobile & computer and i can stor data in my data card
what is formula mv convert to temperture
Describe a time when you anticipated potential problems and developed preventive measures.
Is Hart communicator calibration device or communicating device for transmitter?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)