Answer / pankaj nandasana
As you know....0.2 to 1 kg/cm2 is equal to 3-15 psig..
Generally we are considering this range...reasons are following...
1) Suppose if your have set lower limit at 0 psig, then how you can differentiate zero signal level and pipe breakage..!!!! You can not distinguish two thing..That why we select some elevated range from 0 psig.
2) Our all instrument are producing linear response in the range of 3-15 psig.
3) Pneumatic supply to all instrument is 20 psig..so alway there is bleading of air from instrument..for standardlisation purpose all are considering 3-15 psig..
| Is This Answer Correct ? | 33 Yes | 0 No |
Answer / ashish namdev, bina refinery [
The diaphragm design of all control valves are universal and
the out of the actuators are 3 to 15 psi.When more than the
15 psi pressure is acting to the diaphragm that will lead it
to faulty so we use the 0.2 to 1.0kg/cm2 for control valves.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / s k
because the control valve work within the specified pressure
range of about 0.2 to 1.0 kg/cm2.
| Is This Answer Correct ? | 2 Yes | 8 No |
How vortex sensor used for steam flow measurment can be checked on line i.e without taking out from process line.
what deference between panel earth and systemearth
WHAT IS THE DIFF BETWEEN FREQUENCY AND INTENSITY?HOW IT WORKS IN FLAME SCANNER ?
what is temperature compensation?
Which standard of hazardous area classification used in India?
I HAVE GOT TYPICAL PROBLEM WITH THE TEMP.INDICATION. THE PROBLEM IS THE K-TYPE T/COUPLE OUT PUT IS CONNECTED TO A INDICATOR.THE INDICATION FLUCTUATES SOME TIMES AND SOME TIME IT IS STABLE. WHEN I CHECKED OUT PUT OF T/COUPLE THE MV WILL NOT VARY. WHERE AS INDICATION FLUCTUATES. WHEN I GIVE MV SOURCE TO T/COUPLE EXTENSIONCABLE FROM THE FIELD IT INDICATION IS STABLE. WHEN GIVE MV SORCE TO INDICATOR ITS INDICATION IS STABLE. PLEASE CLARIFY.
Can someone give a detailed chart on the temperature ranges which can be measured by various temperature sensors.
what are the on/off valve precaution?
WHAT IS ANNUBAR?
give classification of transducer based on type of application
How will you calibrate PID controller? explain with example.
0 Answers Jacobs, Sirte Oil Company,
What is the constant voltage unit?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)