why we use 0.2 to 1.0 kg/cm2 output in control valve
Answers were Sorted based on User's Feedback
Answer / pankaj nandasana
As you know....0.2 to 1 kg/cm2 is equal to 3-15 psig..
Generally we are considering this range...reasons are following...
1) Suppose if your have set lower limit at 0 psig, then how you can differentiate zero signal level and pipe breakage..!!!! You can not distinguish two thing..That why we select some elevated range from 0 psig.
2) Our all instrument are producing linear response in the range of 3-15 psig.
3) Pneumatic supply to all instrument is 20 psig..so alway there is bleading of air from instrument..for standardlisation purpose all are considering 3-15 psig..
Is This Answer Correct ? | 33 Yes | 0 No |
Answer / ashish namdev, bina refinery [
The diaphragm design of all control valves are universal and
the out of the actuators are 3 to 15 psi.When more than the
15 psi pressure is acting to the diaphragm that will lead it
to faulty so we use the 0.2 to 1.0kg/cm2 for control valves.
Is This Answer Correct ? | 1 Yes | 2 No |
Answer / s k
because the control valve work within the specified pressure
range of about 0.2 to 1.0 kg/cm2.
Is This Answer Correct ? | 2 Yes | 8 No |
What is DCS?
4 Answers GAIL, Sabic, Trident, Yokogawa,
How we connect a instrument with ground, Give brief explanation with help of diagram?
diff between dead wt calibrator n pressue comparator?
if change the pid in D value so what action.
WHAT IS THE Differance b/w on/off & pid control valve?
What is the reason for not giving very High Proportional Gain Kp in PID Controller?
how we calculate error in percentage when instrument calibrat
NAME ANY TWO PHOTO CONDUTIVE MATERIALS?
HOW DPT WORKS?
what is difference between wheatstone bridge, pirani gauge and strain gauge ??? explain its principle and working
which are types of orifice tap ?
What is full form of hart communicator?