I work on a electronic positioner transmitter 4211 at the
field.I connect my multimeter in series to get the current
output then I calibrate it to 4ma in 0% of position of the
valve and 20ma in 100% position of the valve.My problem is
in the field I get the correct output current based on my
multimeter but in the dcs they only receive 40% in a output
20ma of this positioner.Then I try to simulate in this
analog card and they receive the equivalent percent on the
value that I simulated.Is ther any possibility to reset the
zero and span of this positioner 4211 fisher.And what other
possibility I can do to fixed this.This is my email add (
landicho_randy@yahoo.com )
Answers were Sorted based on User's Feedback
AI card is two wire and the electronic positioner
transmitter is also two wire. I already simulate ma directly
into the card and the DCS receive the equal percentage of
the ma that I simulated.
| Is This Answer Correct ? | 2 Yes | 0 No |
dear friend as per my opinion be sure that your trasmitter
is 4 wire or 2 wire? OR ensure about your ai card 4wire or
2 wire
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sks
you should check that your AI channel might consist of 3
terminals, 1+,1-, COM. this is the facility provided to
connect both voltage(0-10V) or current(4-20ma) analog signal
introducing to AI module/card.
since you are using current i/p(4-20ma) 1- & COM channels
must be looped with 250ohm resistance first. this might
solve your problem.
| Is This Answer Correct ? | 0 Yes | 0 No |
wht is dcs architecture ? can u give example?
wt kind of business we can do by usig PLC?
What is the meaning of wet leg
The Design Calculation of Level Transmitter For Different Structure open & Closed Vessel, Eg. Diff. Level Tx., Capacitance For Continous Operation
Flow tax range 0 to 100 mmh2o ,flow rate 40 tons /hr, I want change flow rate example 42 tons/hr so tx range ?
Instrumentation symbols interpration, P& ID, Logic diagram analysis, Electrical drawing analysis.
Can anybody tell me how to select the size of earthing cable for DCS & PLC system.Please tell me any relevant answer here or mail it to me.
what is the analog input , analog output , digital output, digital input geven to the MSSV , CBD, IBD , START UP VENT , BOILER FEED PUMP , AOP, CEP , ETC
1 Answers Bharat Biotech, TATA,
In field side transmitter voltage droping here no loose connection then what will happen?
How to work & calculated output of the Derivative action in pid controller (Explain Derivative controller)
how to measure draft pressure in transmitter pl. give its single line digram
What is heating effect?
0 Answers Process Control Technologies,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)