I work on a electronic positioner transmitter 4211 at the
field.I connect my multimeter in series to get the current
output then I calibrate it to 4ma in 0% of position of the
valve and 20ma in 100% position of the valve.My problem is
in the field I get the correct output current based on my
multimeter but in the dcs they only receive 40% in a output
20ma of this positioner.Then I try to simulate in this
analog card and they receive the equivalent percent on the
value that I simulated.Is ther any possibility to reset the
zero and span of this positioner 4211 fisher.And what other
possibility I can do to fixed this.This is my email add (
landicho_randy@yahoo.com )
Answers were Sorted based on User's Feedback
AI card is two wire and the electronic positioner
transmitter is also two wire. I already simulate ma directly
into the card and the DCS receive the equal percentage of
the ma that I simulated.
| Is This Answer Correct ? | 2 Yes | 0 No |
dear friend as per my opinion be sure that your trasmitter
is 4 wire or 2 wire? OR ensure about your ai card 4wire or
2 wire
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sks
you should check that your AI channel might consist of 3
terminals, 1+,1-, COM. this is the facility provided to
connect both voltage(0-10V) or current(4-20ma) analog signal
introducing to AI module/card.
since you are using current i/p(4-20ma) 1- & COM channels
must be looped with 250ohm resistance first. this might
solve your problem.
| Is This Answer Correct ? | 0 Yes | 0 No |
how can we measure the level measurement with the help of pressure gauge?
Explain " FAIL SAFE " feature in temp. measurement.
1 Answers Bapco Bahrain Petroleum Company,
What is the role of P(Protional), I(Integral) and D (Derivative) in PID Controller?
What are the maximum packet size of: a) HART b) Profibus DP c)Profibus PA d) DeviceNet e) Foundation Fieldbus
can we control operation of PLC from operator station?
how to calibrate and troubleshooting of leveltroll?
define feed forward control loop with example and drawing?
what is hot loop check and cold loop check.
3 Answers Bapco Bahrain Petroleum Company,
what is temperature compensation?
give classification of transducer based on type of application
How can we calibrate the level interface for Fisher® FIELDVUE® DLC3000?if use water to calibrate and our liquid SG are 0.75 and 1 ,Displacer height=14" and How much should be set SG in trasmitter during calibrate,for URV and LRV how shold be set
wht is dcs architecture ? can u give example?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)