I work on a electronic positioner transmitter 4211 at the
field.I connect my multimeter in series to get the current
output then I calibrate it to 4ma in 0% of position of the
valve and 20ma in 100% position of the valve.My problem is
in the field I get the correct output current based on my
multimeter but in the dcs they only receive 40% in a output
20ma of this positioner.Then I try to simulate in this
analog card and they receive the equivalent percent on the
value that I simulated.Is ther any possibility to reset the
zero and span of this positioner 4211 fisher.And what other
possibility I can do to fixed this.This is my email add (
landicho_randy@yahoo.com )
Answers were Sorted based on User's Feedback
AI card is two wire and the electronic positioner
transmitter is also two wire. I already simulate ma directly
into the card and the DCS receive the equal percentage of
the ma that I simulated.
Is This Answer Correct ? | 2 Yes | 0 No |
dear friend as per my opinion be sure that your trasmitter
is 4 wire or 2 wire? OR ensure about your ai card 4wire or
2 wire
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sks
you should check that your AI channel might consist of 3
terminals, 1+,1-, COM. this is the facility provided to
connect both voltage(0-10V) or current(4-20ma) analog signal
introducing to AI module/card.
since you are using current i/p(4-20ma) 1- & COM channels
must be looped with 250ohm resistance first. this might
solve your problem.
Is This Answer Correct ? | 0 Yes | 0 No |
what is RTV function in in process control?
What is hp & mp seperator .& what is its working principle ?
What is Cryogenic?
I have a close vessel tank which is under vaccum when in running condition so pl. Provide it's range for dp type tx whose flange to flange distance is 440 mm and density is 1
In which principle Woodward Governor 505 work in power plant? What are the input of Woodward governor 505
suppose there is gas flow meter I want to know weather meter calibration is done at high pressure or low pressure? pls justify.
what is the pressure in the tank when its level of liquid is 1.5 meters when its total capacity is 2 meters
In s7-200 we use HMI TD-200C , what that C stands for........ plz reply
why relays are used with plc?
explain Cascade Control strategy with the help of a block diagram. also exlain its working in a distillation column
what is upstream and downstream in liquid flow?
what is the difference between(Flame proof/Explosion proof)& Fire proof instruments.Both are same or different & if different in which way because the transmitter which have approved ATEX flame proof enclouser but it use PTPE O ring & PTFE Head Gasket,so its (fire safe/fire proof)????????