I work on a electronic positioner transmitter 4211 at the
field.I connect my multimeter in series to get the current
output then I calibrate it to 4ma in 0% of position of the
valve and 20ma in 100% position of the valve.My problem is
in the field I get the correct output current based on my
multimeter but in the dcs they only receive 40% in a output
20ma of this positioner.Then I try to simulate in this
analog card and they receive the equivalent percent on the
value that I simulated.Is ther any possibility to reset the
zero and span of this positioner 4211 fisher.And what other
possibility I can do to fixed this.This is my email add (
landicho_randy@yahoo.com )
Answers were Sorted based on User's Feedback
AI card is two wire and the electronic positioner
transmitter is also two wire. I already simulate ma directly
into the card and the DCS receive the equal percentage of
the ma that I simulated.
| Is This Answer Correct ? | 2 Yes | 0 No |
dear friend as per my opinion be sure that your trasmitter
is 4 wire or 2 wire? OR ensure about your ai card 4wire or
2 wire
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sks
you should check that your AI channel might consist of 3
terminals, 1+,1-, COM. this is the facility provided to
connect both voltage(0-10V) or current(4-20ma) analog signal
introducing to AI module/card.
since you are using current i/p(4-20ma) 1- & COM channels
must be looped with 250ohm resistance first. this might
solve your problem.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is different between 2,3&4 wire rtd and how much maximum distance using plc to field.
in natural gas indirect water bath heater,how to prevent the problem of backfire from firetube during ignition...becoz of this backfire performance of wbh is going low.
WHAT IS A CALLIBRATION? WHAT IS MEEAN BY LOOP CHECKING INCLUDES PRESURE, THERMOCOUPLE,TT,DT?
which type signal come control valve
why we take 4 to 20 mA as out put of every instrument like pressure transmittre ?why we cant take 0 to 20mA as output?
what are the installation requirement is common to all flow meter when volumetric flow rate is being measured
What is the difference between local indicator(flow) and flow indicator?
What is negative range in transmeter?
What is scan time of PLC?
What is use of condensate pot
5 Answers Alstom, Petrocil, Samsung,
1. what is modbus cable? 2. what kind of communication we are using for the interface of DCS, ESD and Third party cabinets? 3. What is serial communication and peer to peer communication?
in transmiters(rose mount) how to check output 4-20ma ? and input 24v? i need exact explanation?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)