How we can do the linearity test for Bently Naveda
Vibration Probe?
Answer / ahmed sabry
first, we have 3 main types of Bently vibration probes:
1 - Proximity probe
2 - Accelerometer probe
3 - Key phasor probe
For proximity probe, we have 2 types:
1 - displacement probe for axial forces measurement.
2 - velocity probe for radial forces measurement.
Both tyes of probes are calibrated using a suitable calibration kit supplied by the vendor, the calibration kit simulate the shaft vibration and can be used to check/adjust the probe and the monitor.
I have a practical experience with 3300 system which give the output through "proxomiter" from terminals output & ground - for normal case it has to give "-10 vdc" and we have 200 mv for every 1 mil diplacement.
This is an example of used calibration kit:
http://www.ge-mcs.com/download/sensors-and-transducers/141580.pdf
==========
If we need to Check/calibrate the rest of the vibration loop (monitor check), We will need a function generator & multimeter.
For the monitor we will inject in the Monitor card by the function generator a combination voltage of -7 dc voltage with AC voltage with suitable freq.(follow the manual to specify the values of AC, DC and freq.).
For axial vibration monitor we will vary the DC amplitude and check the results on the monitor.
For radial vibration monitor we will vary the AC amplitude and check the results on the monitor.
Best of luck
Ahmed Sabry
Instrumentation & Control Engineer
Mob: +2 0122 1367310
Is This Answer Correct ? | 18 Yes | 1 No |
how we convert Mili ampere to temp txt,level txt,flow txt,pressure txt range value
what is cavitation ?
Foe selecting control valve if i have the min,normal & max data of flow rate,inlet pressure& outlet pressure,inlet tem.&density than how can i assure that these data are correct,pl. let me know if therew there is any method to check it.& also how we assure that the Cv we get from this data is suitable for valve for controlling require flow.
what is the pressure in the tank when its level of liquid is 1.5 meters when its total capacity is 2 meters
Why went
what is the standard controll pressure
how to change 4 wire rtd transmitter into a 3 wire rtd transmitter? as our transmitter is working for 4 wire rtd, what should do for working on 3 wire rtd transmitter
what is the difference between transmitter and converters?
How will you change the action of a control valve?
Will Intergraph support SmartPlant Instrumentation in an AutoCAD or MicroStation environment on a long-term basis?
What is duty of as-built engineer.
how to calibrate the radar transmitter for measuring the exact tank level if tank is having agitator moving continiously because due to agitator tank surface level will vary every time.