how to calibrate the radar transmitter for measuring the
exact tank level if tank is having agitator moving
continiously because due to agitator tank surface level
will vary every time.
Answers were Sorted based on User's Feedback
Just increase the damping on the radar's 4 to 20mA output.
This should stabilize the output, even if the local display
still jumps around.
In the DCS there is also damping that will help with the
input from the radar.
You will never be able to measure an "exact" level in a
turbulent application like this so the best you can do is to
use the average over a period of time and that is what the
damping does. It smooths out the ripples in the output by
taking samples of the level measurement and then give a
average output.
Good luck
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / jayesh
there are sensors available which allows you to select the
nature of fluid like weather it is turbulent of steady so
according to that it adds the damping factor to it and
gives you out put
| Is This Answer Correct ? | 3 Yes | 0 No |
I will attend an interview with GasGas company for a position of Instrument Technician ( Offshore )in next month can anyone tell me what questions they will ask. Thanks in advance.
In Boiler Drum Level- Level control valve how can it tuning (PID)?
why we are using -24 vdc in plc?
what is maximum vaccume?
I HAVE GOT TYPICAL PROBLEM WITH THE TEMP.INDICATION. THE PROBLEM IS THE K-TYPE T/COUPLE OUT PUT IS CONNECTED TO A INDICATOR.THE INDICATION FLUCTUATES SOME TIMES AND SOME TIME IT IS STABLE. WHEN I CHECKED OUT PUT OF T/COUPLE THE MV WILL NOT VARY. WHERE AS INDICATION FLUCTUATES. WHEN I GIVE MV SOURCE TO T/COUPLE EXTENSIONCABLE FROM THE FIELD IT INDICATION IS STABLE. WHEN GIVE MV SORCE TO INDICATOR ITS INDICATION IS STABLE. PLEASE CLARIFY.
what should be the distance of vibration sensor & to the point where vibration to be measured Ex turbine axial displacement
Why do we need to install hook-up line differential pressure type level transmitter when the differential pressure type level transmitter with capillary are available?
what is relation between electronics&instrumentation
in the construction field why hook up s.s.tubing for transmitter using upto 6mtrs of closed loop, but y not open loop nomore restriction
Single acting ON-OFF valve. it is air to open. when sov energized , valve will be open, so during that if air fail then what will be the condition of valve ( open or close ) ???
What is the constant voltage unit?
Is there any temperature compenasation for the air flow from FD fan & SA fans which supplies air to the Boiler?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)