Answer / tathagata
If single phase motor is supplied by ac supply, it will rotet
because single phase motor are universal motor. So it work
for both AC & DC.
But the DC supply must be less than its AC rating, because
in DC there is no reactant .
I=V/(R+jX) (AC)
I=V/R (DC)
So current is vary high which may burnt out the winding.
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / santosh
torque in single phase induction motor is produced due to rotating magnetic field. if this motor is fed from dc, the rotating magnetic field is absent and the machine will not run.
also in the absence of reactance in DC, the machine will try to draw high current which will damage the winding.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / alan jenkins
In a nutshell it depends what type of motor it is, some motors with a wound rotor and brushgear will run on AC and DC, however AC induction motors will not rotate, the DC current will have a locking effect on the rotor, hence DC injection braking (anyone heard of that ?)leaving a DC current on these motors for any length of time will heat up the windings.
| Is This Answer Correct ? | 0 Yes | 0 No |
Sir we have 12.5 MVA(110/11KV) transformer (Y-Y) connected,which tripped showing earth fault,when we charged transformer it stood OK ,but on connecting 11 KV feeders it tripped showing earth fault.our service engineers found that the B phase and R phase phase connecting to neutral broken from HV OLTC(on load tap changer),and R phase and Neutral is ok.Dissolved gas analysis shows that accetline content is high,tan delta value is 12.My dout is it is an internal fault of transformer,why REF or diffrential relay is not acted?
what is the working of hydrent system.
How many loops can be provided in a circuit as per IS rules.?
what is Use of Stones/Gravel in electrical Switch Yard??
WHY THE RATINGS OF THE TRANSFORMER IS 33KV WHY NOT OTHER???
is there any difference in reading or error in value, if we connect the R phase in Y terminal and Y phase in R terminal of electronic energy meter of 11 kv feerders???
What happened ,If 3 phase clearance not maintained in 33KV Line,11KV LIne etc?
what is the difference b/w pvc cu conductor and cu breaded wire..?
discuss thyrister convertor type of AVR.
How many double suspension hardware fittings are required on a double circuit transmission tower?
WHAT ARE THE EFFECTS OF SERIES RESONANCE AND PARALLEL RESONANCE ON THE CIRCUITS PARAMETERS?
why do we use UPF watt meter in short circuit test of the transformer and LPF watt meter in open circuit test of the transformer
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)