What is the basic difference between 90% stator earth fault
and 100% stator earth fault, and its phenmenona?
Answers were Sorted based on User's Feedback
As neutral of the generator is approched, the driving
voltage available between the fault point and the neutral
is very low & hence not detectable. So last 5% of the
generator winding remains nprotected with the conventional
schemes of E/F protection. that is why it is called 95%
stator earthfault protection. For covering the rest of 5%
winding other techniques like 3rd harmonic principle ets
are available.
| Is This Answer Correct ? | 10 Yes | 1 No |
This is an application with power plant genrator protection.
In early 1950-75,only 90% stator earth fault protection
used for Generator Stator winding.
GE,westinghouse,hitahachi,GEC,BBC,KWU.ON 1975 ONWARDS,
THEN 100% STATOR EARTH FAULT DEVELOPED USING OPEN DELTA
VOLTAGE OFGENERATOR AND USING FIRST AND THIRD HARMONIC
BRIDGE.
WEST AND EUROPE,INDIA USED GENERATOR NETRAL GROUNDING
TRANSFORMER AND ON SECONDARY OF THIS TRANSFORMER90%STATOR
EARTH FAULT PROTECTION IS USED.
FOR 100% STATOR EARTF FAULT USE OPEN DELTA VOLTAGE.
Russian practice is use voltage transformer for generator
neutral gounding.
when I was DISCUSSING this with european manufacturer, they
want to delete 100% protection.In a generator it is meaning
less.fault is fault.It is time consuming for repair.
As a new challenge-generator manufacture claim 100%
availabilty of Generator with VIP.
/MICADOUR ELASTIC INSULATION. In gas turbine a single
generator rating is selected for single shaft gas turbine
and steam turbine. upto 275MW. AND 400MW
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / saka
90% Stator earth fault protection achieved through NGR and
100% Stator earth fault achieved through REF ( NGTR )
| Is This Answer Correct ? | 1 Yes | 6 No |
Answer / k.prakashchandra
90% means providing protection for 90% of stator winding and
100% means for entire winding
| Is This Answer Correct ? | 4 Yes | 10 No |
what happens if sf6ckt breaker gas pressure is high or low about the actual rating of gas pressure(5kg/cm2)
Why different Pressure switch used in marine boiler water circulation system
why transformer are rated in KVA not in watt?
what is the function of choke and starter in a tube light??
How to test the Secure Elite 440 Multi function meter working condition.
0 Answers Sadanand Constructions,
How size of Earth Strip is determined for a particular Fault current.
If a ACB breaker is tripping and closing problem, then what will we check internal..?
what is the mazor difference between the induction transformer and synchonous motor?what is the similarity between them?
Brief use of isolation transformer & how it works.
wath is this mining of bts
What will happen if i connect the delta winding motor to star input.
whether the battery is voltage source or current source?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)