what is o2 analyzer and how it measured ,what is the role of
this analyzer in cfbc boiler...
Answers were Sorted based on User's Feedback
O2 analyzer is used in all types of boilers like CFBC and
AFBC etc..role of this analyzers to measure the O2
concentration after the ECONOMIZER ,it is a normal value like
(3 to 4) no problem ,if any variotions obeserved based on
that value we can increase/decrease SA fan air into the boiler
Is This Answer Correct ? | 20 Yes | 1 No |
Answer / msp
:- If analyzer showing wrong on DCS than first I will
forced the analyzer value on the DCS if any tripping taken
from it.
Through the Multimeter checked the value 4 to 20 mA on DCS
or same on field As per define range in the DCS as well as
analyzer transmitter. If all things are correct than its
calibration was got disturbed. For the calibration
1 For the calibration we need sample gas and instrument air.
2 Connect the both input instrument air and sample air
through the rotameter for flow control of the both air and
sample gas.
3 Power on the analyzer and communicate hart communicator
with the analyzer.
4 For the zero calibration apply the sample gas with the
help of rotameter for flow control on the analyzer. And
press enter on the zero calibration on the hart
communicator.
5 For the span calibration apply the Instrument air with
the help of rotameter for flow control on the analyzer. And
press enter on the span calibration on the hart
communicator.
After calibration save the setting with the help of the
hart communicator.
And cross checked the same 4 to 20 mA by given the
instrument air and sample gas accordingly.
Is This Answer Correct ? | 11 Yes | 0 No |
GIVE BRIEF DESCRIPTION ABOUT "DCS"
what is The specifications for oriface instalation
how to calibrate control valves & power cylinders & ultra sonic level transmitters
i am having information technology branh ....... can i prepare for psu exam
few questions on RS 232,1 question on relationship of impedance and turns ratio, many questions on flowmeters
How do Foundation Fieldbus works? how the Communication Carries out from Foundation field bus,Field Devices and Controller? Were it's Application in the Field? For Which Signals this is Used? PLease Find this answer for this Question Detaile wise because i want to clear the Concept Regarding Foundation Field Bus,if Possible please attach the link of Document with Contails Diagramatic So that more esier for me.
How many problems can be occurring in solenoid valve? And how it can be rectified?
How much should be the values and/or percentages of these given below factors for a good controller ? Steady state error Delay Rise Time Overshoot Peak Time Settling Time Damping Oscillations & vibrations thanks
what is span value and zero ? and how set ?
what is the diffrence between mmwc and kg/cm2 for pressure measurment when we are using mmwc and when kg/cm2 and why????? ?? what is the reason
19 Answers Ecoboard, Jindal, Sepco,
How to check the SCAN time of DCS ,n dont give therotical answers .How to check the SCAN time of DCS during FAT?
What is mean by Ethernet, Device net and Control net? For what application we are using these?