If i consider your 644kW load as a motor then,
I Assumed some parameters are:
644kW Motor, Power Factor - 0.9, Efficiency - 0.9, Load
Connected Voltage - 415V Then,
I = (644*1000) / (1.732*415*0.9*0.9) = 1106Amps
Considering 20% Margin = 1106 * 1.20 = 1327Amps
Conclusion:
So, We can choose Breaker rating is higher than that
1327Amps. Generally no one use the MCCB breaker above
800Amps. So, we can prefer the 1600Amps VCB Breaker for that
644kW Load.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / antaratara ghosh
assuming the load as motor,operating voltage as 415 V,pf
as .85, efficiency as .95,
rated current, Ir= (644)/(1.732*0.415*0.85*0.95)
= 1110 A (approx)
now considering VFD starting for the motor,
starting current, Ist= 2*Ir
= 2220 A
considering margin of 20%, maximum current flowing =
2220*1.2 = 2664 A
Since MCCB are not used above 630 A in India, you have to
go for 3150 A (which is just greater than 2664 A and
available in market) ACB...
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / ahmed raza
Formulla for calculation of breaker is...
Total load in Watts/380(voltage)*0.8(pf)*1.732(delta to Y
conversion)
So
= 644/380*0.8*1.732
= 1223.10
we can say
= 1250AMPs breaker should be use....
| Is This Answer Correct ? | 0 Yes | 3 No |
what is the calculation of power factor?
which tap of the transormer you will use in critical condition(worst)?
Why the transmision line are 11,33,63,132kv?
when a pure dc signal is sent through a moving iron meter, what will it read?? dc or rms?? when a variable dc signal is sent through a moving iron meter, what will it read?? dc or rms??
1.Why hydrogen used for cooling in generators 2.Why electrical equipment protected by ground 3.Why earthing for transmission line 4.What is rms value of half wave rectified square wave. If Rms value of actual wave 2amps.
why 5kW motor becomes unbalance if its relay trip 1st time and its set value is 7.0 A
How to calculate the size of the cable? for exp i want to use the load of 10HP
What are types of HT Motors.
what happens to the speed of a DC series motor when series field winding is removed?
What is non-minimum phase transfer function?
why neutral is neccessary?
what size of copper busbar use for 11kv 630A
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)