for 644KW load which MCCB should i use
Answers were Sorted based on User's Feedback
If i consider your 644kW load as a motor then,
I Assumed some parameters are:
644kW Motor, Power Factor - 0.9, Efficiency - 0.9, Load
Connected Voltage - 415V Then,
I = (644*1000) / (1.732*415*0.9*0.9) = 1106Amps
Considering 20% Margin = 1106 * 1.20 = 1327Amps
Conclusion:
So, We can choose Breaker rating is higher than that
1327Amps. Generally no one use the MCCB breaker above
800Amps. So, we can prefer the 1600Amps VCB Breaker for that
644kW Load.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / antaratara ghosh
assuming the load as motor,operating voltage as 415 V,pf
as .85, efficiency as .95,
rated current, Ir= (644)/(1.732*0.415*0.85*0.95)
= 1110 A (approx)
now considering VFD starting for the motor,
starting current, Ist= 2*Ir
= 2220 A
considering margin of 20%, maximum current flowing =
2220*1.2 = 2664 A
Since MCCB are not used above 630 A in India, you have to
go for 3150 A (which is just greater than 2664 A and
available in market) ACB...
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / ahmed raza
Formulla for calculation of breaker is...
Total load in Watts/380(voltage)*0.8(pf)*1.732(delta to Y
conversion)
So
= 644/380*0.8*1.732
= 1223.10
we can say
= 1250AMPs breaker should be use....
| Is This Answer Correct ? | 0 Yes | 3 No |
Which type of drive is advantageous AC or DC and why?
what is Aircraft earthing and what does it do?
Difference between SFU & FSU with advantantages & drawback?
When connecting a loaded powerplant to the Huge grid,what are the factors to be considered and how the VAR flow will affect the system?
What are the differences between single phase and three phase?
why cant we use earth as neutral at home whereas neutral is actually grounded at transformer end?
Describe the colour rendering properties of i) tungsten filament lamps ii) tubular fluorescent lamp
how are reversing the direction of dc motor
Dear all, I want to use Induction motor to open and close a 1 ton door. How much power do I need. Thanks
What is the actual formula for transformer short circuit test? below i given rating of the transformer.. 1000KVA, pri 11KV, Pri amp 56A. %Z 5.95..
what is the Space heater? why using in Electrical motor?
induction motor. we have a three phase supply from diffrent source like R= transformer. Y = DG sets. B = ups. if motor is runing.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)