If i consider your 644kW load as a motor then,
I Assumed some parameters are:
644kW Motor, Power Factor - 0.9, Efficiency - 0.9, Load
Connected Voltage - 415V Then,
I = (644*1000) / (1.732*415*0.9*0.9) = 1106Amps
Considering 20% Margin = 1106 * 1.20 = 1327Amps
Conclusion:
So, We can choose Breaker rating is higher than that
1327Amps. Generally no one use the MCCB breaker above
800Amps. So, we can prefer the 1600Amps VCB Breaker for that
644kW Load.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / antaratara ghosh
assuming the load as motor,operating voltage as 415 V,pf
as .85, efficiency as .95,
rated current, Ir= (644)/(1.732*0.415*0.85*0.95)
= 1110 A (approx)
now considering VFD starting for the motor,
starting current, Ist= 2*Ir
= 2220 A
considering margin of 20%, maximum current flowing =
2220*1.2 = 2664 A
Since MCCB are not used above 630 A in India, you have to
go for 3150 A (which is just greater than 2664 A and
available in market) ACB...
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / ahmed raza
Formulla for calculation of breaker is...
Total load in Watts/380(voltage)*0.8(pf)*1.732(delta to Y
conversion)
So
= 644/380*0.8*1.732
= 1223.10
we can say
= 1250AMPs breaker should be use....
| Is This Answer Correct ? | 0 Yes | 3 No |
why can't we increase the voltage by increasing the field voltage in order to get higher voltage.so that we can eliminate step up transformer
In general bus riser follows the bus section in SWGR. What are impacts if bus section follows bus riser?
What type of DC Generator is used for Arc Welding purposes?
why HT voltage rating in multiple of 11
If we connect a motor and generator together (I mean that the generator gives the motor electricity and the motor gives the generator movement) regardless the losses. Will the generator still generate and the motor still move?
Whats the difference btwn a latch, port,data bus buffer? Do they all not hold data in d flip flops??
Why infinite busbar has zero resistance and high mechanical inertia?
Ohms law explain
y we use neutral,all r told its used to for closed path..k its a just used to closed path,in a transmission line y we put same conductor used n both phase and neutral..if we use less than phase conductor in neutral mean we ll reduce cost its right r wrong..if we use mean any problem occur in transmission line..
what is meant by insulation voltage in cables? explain it?
how to find out speed of single phase motor
by using pump duty, how we will can calculate the motor duty(KW)? is there any standard or formula.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)