for 644KW load which MCCB should i use

Answer Posted / karthik ccel

If i consider your 644kW load as a motor then,

I Assumed some parameters are:
644kW Motor, Power Factor - 0.9, Efficiency - 0.9, Load
Connected Voltage - 415V Then,


I = (644*1000) / (1.732*415*0.9*0.9) = 1106Amps
Considering 20% Margin = 1106 * 1.20 = 1327Amps

Conclusion:
So, We can choose Breaker rating is higher than that
1327Amps. Generally no one use the MCCB breaker above
800Amps. So, we can prefer the 1600Amps VCB Breaker for that
644kW Load.

Is This Answer Correct ?    6 Yes 3 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Whether it is possible to measure energy at the input of rectifier transformer (12 pulse with very high odd harmonics)

1474


Testing procedure of DG alternator stability test

949


Is there any problem about which the drive (inverter) doesn't show/display the alarm and/or fault but instead of this , it doesn't work ? I want to know that could there be any kind of problem in the drive when the drive doesn't display the alarm and/or fault ?

1520


what are the advantages and disadvantages of speed control of 3 phase induction motor by varying frequency explain with drawing

2182


why electron produce magnetic field when it is in motion?

1695






why we use two slope(differential & restraining) in differential relay.but in busbar protection differential we are using only one slope?please explain

1735


what is the breaking capacity and making capacity of circuit breaker and how

1597


what are the breakdown voltage rating of mini- curcuit'transfarmer!

1669


Dear sir, How to calculate 3.5 core pvc aluminium armoured cable meter wise carrying amps rating.Please give the solution with a good example.

1313


I have c license but I don't know eligibility of Max Kilo Volts under the electrical licensing board.

1220


Explain the role of a car driver as one of a feedback mechanism.

746


What is the name of the winding to which supply is given?

701


how indusrial diesel generator work

1473


how we can calcultae the short circuit level for bus bar

1735


How to calculate main incomer rating of APFC Panel ? Let's say i want to find main incomer for 11kV, 1000kVAR Panel.

1233