how to calibrate differential pressure switch
Answers were Sorted based on User's Feedback
Differential pressure switch has two sensing ports. Hi and
Lo, Suppose set point of differential pressure switch is
30 PSI. Connect the pressure source at hi side of switch.
Leave Lo side (No any connection or any supply to low side)
Connect multimeter at switch terminals. Apply pressure at
high side. When pressure will reach 30 PSI, Switch will
operate and will change its contacts and also will be
indication at meter.
Suppose switch Low side is faulty, then apply 30 PSI at
High side and also apply low side pressure (5 to 10 PSI),
switch contacts should change, which indicate switch is
working.
aftabmazari@yahoo.com
| Is This Answer Correct ? | 21 Yes | 2 No |
Answer / suresh m (fcri)
In most pressure switches, the set-point is adjustable.
During calibration, pressure is applied slowly near the set-
point, and usually a continuous reading Reference sensor
(or a calibrated dial-gauge)is used. During increasing
pressure, when set-point is reached (or crossed), if the
switch does not show contact change, then the knob (or
spring / bolt) is adjusted for correct action.
The test is repeated to confirm the switching of contacts
at desired pressure.
The pressure is raised slowly to a value above the set-
point during the test even as we observe switch-over
pressure. Later the switch change-over back to initial
state is also confirmed as we lower the pressure below the
set-point pressure.
| Is This Answer Correct ? | 8 Yes | 0 No |
What is pressure,What is temperature,What is flow,What is level
What is trim material . Why it is known as trim.
plz... clarify my answer, how to calibrate vaccum (DP)leveltransmitter,it is hart. (digital).DETAILS:(coloumn)closedtank height 2650mm,and tx range is 0-1500mmH20.
define SIMULATION a and what is the need of it
I have transmitter of range -20 to -5 kpa.if it is possible to zero trim with atmospheric pressure,means HP and lp having no pressure...what will get after zero trim and it is the right way.....plz give me reply ....
Using your own examples solve a problem involving normal table. (experimental method and analysis)
In the field and in the control room different power supplies if used How to handle the ground
How to find out turn down ratio of Pressure transmitter?
How can we check Zero of DP type Level Transmitter onside?
why use 50% lel methane gas concentration for gas detector calibration instead of 60% lel gas concentration whereas the hi alarm set at 60% lel.
how to define range of dp level xmeter in open tank
Explain how thw analog to digital converter works with the circuit diagram
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)