Suppose an electric motor with a controller is not working.
What is the sequence of testing you will do in your
troubleshooting?
Answers were Sorted based on User's Feedback
* 1st check the power supply switch whether on or off
* then Check the all wiring connections may be wire disconnected or there is any loose connection(OFF the switch).
* smell the component whether it is heated or not and touch to experiance the heat(OFF the switch).
* replace the controller/motor with new one to detect fault present in which part.
| Is This Answer Correct ? | 25 Yes | 2 No |
Answer / ishwar shivanand dematti
* Check the all wiring connections some wire disconnected.
* check the power supply is come or not come
And Check the any loose connections
| Is This Answer Correct ? | 8 Yes | 9 No |
i am studying in final year can i allowed for 23rd UES of Indian army
What is difference is of VSD,VFD,VSDS, are they the same as the direct current to control dc using above mention
why anti pumping relay is not given to tripping coil of the breaker? why only to closing coil?
what is the differnce of STATIC ENERGY METER FROM ordinary energy meter?
My question is whether bellow formula is correct to find bus size for 46kA for 0.5 second & what is RT in bellow formula. formula to calculate the size of busbar to withstand the thermal stresses due to currents with duration of 0.2 sec to 5 sec. Sp = RT( I x I x t) / K Where Sp – is the cross sectional area of bus bar in millimeters. I - is the value of AC fault current. t - is the operating time of disconnecting device in seconds. K – is the factor depending on the material of the conductor, insulation and initial and final temperature. Value of ‘k’ for copper is 143.
What happen when ct secondary are open circuited? why same thing is not happen in ordinary transformer?
Define settling time.
How can you measure the signal from the PT100 sensor?
Why we use Y-Y connection in power transformer (8-10 MVA, 132 kV to 11 KV)and D-y in distribution transformer (2 MVA, 11 KV to 440 Volts)?
We have 5 Distribution sections with variable loads&We have 3 Gensets(500kva,380kva&250kva) our total load is between 400kva to 600kva. so how could we connect 3gensets.
what is power and what is watts detailed description and formulas
for high freq ac,why we first convert AC to DC and then DC to high freq.AC
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)