For a certain load i need 100kw load ,In that case what
rating mccb should i use?
Answers were Sorted based on User's Feedback
Answer / chintan patel
It can be different for DC , 1phase AC , 3 phase AC , systems,
Lets calculate for all ,
1 ) For DC ( you have not mentioned Voltage but considering 230 V )
100 kw means 100000 watt
formula for DC power p= vi
100000= 230xi
i=100000/230= 434 amp
we always use current rating of the mccb is 1.5 times of full load current so we can use 434x1.5= 652 amp.
( if system is not running on full load select 630 Amp MCCB, if its on full load select 800A )
2 ) For 1phase AC,
Power: P = V I cos phi ( cos phi is power factor is not known assume 0.8 )
100000 W = 230 x I x 0.8
I = 543 Amp
we always use current rating of the mccb is 1.5 times of
full load current.
mccb required 543 Amp X 1.5 = 815 Amp
select 800 Amp MCCB
3)
If load is 3 phase AC ,
Power P = sqrt(3) x V x I x cos phi
100000 w = 1.73 x 415 x I x 0.8
I = 174
we always use current rating of the mccb is 1.5 times of
full load current.
mccb required 174 Amp X 1.5 = 261 Amp
( if system is not running on full load select 250 Amp MCCB,
if its on full load select 315 A )
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / kalyan sharma
for 100 kw we will use 3 phase supply inplace of single
phase.
use formula p= 1.732 vi cosphi
100= 1.732*0.415*0.8*I
I = 174 amp
we always use current rating of the mccb is 1.5 times of
full load current so we can use 250 AMPs MCCB.3P/4P.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / rajat
for 100 kw means 100000watt
use formula p= vi
100000= 230xi
i=100000/230= 430 amp
we always use current rating of the mccb is 1.5 times of full load current so we can use 430x1.5= 645 amp
| Is This Answer Correct ? | 5 Yes | 4 No |
Answer / r g walia
for 100kw load required 630 amp mccb will be used.
| Is This Answer Correct ? | 2 Yes | 3 No |
What meant by XLPE cable
how is working d.c amps meter?how to connect the dc ammeter inthe circuite?
How much water ( Kilo Liters) a submercible pump of 35 HP can lift from Borewell of 6" and 900 feet dip.
Suppose an electric motor with a controller is not working. What is the sequence of testing you will do in your troubleshooting?
why three phase three wire system probably did'nt have neutral
Calculate the demand in KVA for a three phase 440V power source drawing 1100A current
According to underground cables a) stress b/w sheath & conductor is high b) inrush of core & conductor
0 Answers CDS, Engineers India Limited, TNQ,
Hi Recently I got one formula that is Impedence of Xformer = Rated KVA/Root 3 * secondry voltage OF Xformer. Is it Right??????
How could I get a certificate of competency as Electrical Supervisor? I have completed By BTech in Electrical this year(2012) for VJTI Mumbai Maharashtra. Is it compulsory to be produced while joining?
in 33kv/11kv stepdown t/f why should we use Star point
how to test an MCB
CFL lamp is what type of load?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)