For a certain load i need 100kw load ,In that case what
rating mccb should i use?
Answers were Sorted based on User's Feedback
Answer / chintan patel
It can be different for DC , 1phase AC , 3 phase AC , systems,
Lets calculate for all ,
1 ) For DC ( you have not mentioned Voltage but considering 230 V )
100 kw means 100000 watt
formula for DC power p= vi
100000= 230xi
i=100000/230= 434 amp
we always use current rating of the mccb is 1.5 times of full load current so we can use 434x1.5= 652 amp.
( if system is not running on full load select 630 Amp MCCB, if its on full load select 800A )
2 ) For 1phase AC,
Power: P = V I cos phi ( cos phi is power factor is not known assume 0.8 )
100000 W = 230 x I x 0.8
I = 543 Amp
we always use current rating of the mccb is 1.5 times of
full load current.
mccb required 543 Amp X 1.5 = 815 Amp
select 800 Amp MCCB
3)
If load is 3 phase AC ,
Power P = sqrt(3) x V x I x cos phi
100000 w = 1.73 x 415 x I x 0.8
I = 174
we always use current rating of the mccb is 1.5 times of
full load current.
mccb required 174 Amp X 1.5 = 261 Amp
( if system is not running on full load select 250 Amp MCCB,
if its on full load select 315 A )
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / kalyan sharma
for 100 kw we will use 3 phase supply inplace of single
phase.
use formula p= 1.732 vi cosphi
100= 1.732*0.415*0.8*I
I = 174 amp
we always use current rating of the mccb is 1.5 times of
full load current so we can use 250 AMPs MCCB.3P/4P.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / rajat
for 100 kw means 100000watt
use formula p= vi
100000= 230xi
i=100000/230= 430 amp
we always use current rating of the mccb is 1.5 times of full load current so we can use 430x1.5= 645 amp
| Is This Answer Correct ? | 5 Yes | 4 No |
Answer / r g walia
for 100kw load required 630 amp mccb will be used.
| Is This Answer Correct ? | 2 Yes | 3 No |
What is measurement?
Dsitrubution transformer minimum IR value
IF ANYONE HAVE ANY QUESTION ASK ME AT MY MAIL anmol.bhardwaj5@gmail.com
Can we parallel lise the secondary side of the two similiar transformers with same voltage ration, imp, but with different vector groups.. ( for ex. 11 KV / 6.6KV two trfs but different vector groups can we parallelise both of them ,, what happens if we parallelise them
What is creepage distance..... what will be the value for different voltage level
We are installing a 1.6 MVA transformer at our crusher plant and the feeder of HPSEBL is 2 km away at substaion . and a VCB is installed in the substaion which is 2 km away from transformer so we need another VCB near the transformer.
what is surge voltage and surge current?
a 650 KVA diesel generator is 1500 rpm, voltage is 415V n full load amps is 805 something,when are applied load more than 400 amps it's voltage is dropping, what is the reasons...?
If a fan get trip and run in reverse direction due to system flow. Now in this condition during starting how can a VFD bring this negative speed to zero and later run in forward direction?
2 Answers Aditya Birla, Siemens,
the max. power will be transferred if …… a) sending end vol. is high b) receiving end v is high c)…….. d) corona loss is least
2 Answers Engineers India Limited,
what is the size of cable for 15kw motor and 85 meter cable length using with vfd
Why inductor short on dc and capacitor allow to flow ac?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)