Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


For a certain load i need 100kw load ,In that case what
rating mccb should i use?

Answers were Sorted based on User's Feedback



For a certain load i need 100kw load ,In that case what rating mccb should i use?..

Answer / chintan patel

It can be different for DC , 1phase AC , 3 phase AC , systems,

Lets calculate for all ,

1 ) For DC ( you have not mentioned Voltage but considering 230 V )

100 kw means 100000 watt

formula for DC power p= vi

100000= 230xi

i=100000/230= 434 amp

we always use current rating of the mccb is 1.5 times of full load current so we can use 434x1.5= 652 amp.
( if system is not running on full load select 630 Amp MCCB, if its on full load select 800A )


2 ) For 1phase AC,

Power: P = V I cos phi ( cos phi is power factor is not known assume 0.8 )

100000 W = 230 x I x 0.8
I = 543 Amp

we always use current rating of the mccb is 1.5 times of
full load current.
mccb required 543 Amp X 1.5 = 815 Amp
select 800 Amp MCCB

3)

If load is 3 phase AC ,

Power P = sqrt(3) x V x I x cos phi

100000 w = 1.73 x 415 x I x 0.8
I = 174

we always use current rating of the mccb is 1.5 times of
full load current.
mccb required 174 Amp X 1.5 = 261 Amp

( if system is not running on full load select 250 Amp MCCB,
if its on full load select 315 A )

Is This Answer Correct ?    3 Yes 0 No

For a certain load i need 100kw load ,In that case what rating mccb should i use?..

Answer / kalyan sharma

for 100 kw we will use 3 phase supply inplace of single
phase.

use formula p= 1.732 vi cosphi

100= 1.732*0.415*0.8*I

I = 174 amp

we always use current rating of the mccb is 1.5 times of
full load current so we can use 250 AMPs MCCB.3P/4P.

Is This Answer Correct ?    3 Yes 1 No

For a certain load i need 100kw load ,In that case what rating mccb should i use?..

Answer / rajat

for 100 kw means 100000watt

use formula p= vi

100000= 230xi

i=100000/230= 430 amp

we always use current rating of the mccb is 1.5 times of full load current so we can use 430x1.5= 645 amp

Is This Answer Correct ?    5 Yes 4 No

For a certain load i need 100kw load ,In that case what rating mccb should i use?..

Answer / r g walia

for 100kw load required 630 amp mccb will be used.

Is This Answer Correct ?    2 Yes 3 No

For a certain load i need 100kw load ,In that case what rating mccb should i use?..

Answer / siddhart jha

mccb of 250 A/440V MUST BE USED FOR THAT.

Is This Answer Correct ?    0 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

What is measurement?

0 Answers  


Dsitrubution transformer minimum IR value

1 Answers  


IF ANYONE HAVE ANY QUESTION ASK ME AT MY MAIL anmol.bhardwaj5@gmail.com

0 Answers  


Can we parallel lise the secondary side of the two similiar transformers with same voltage ration, imp, but with different vector groups.. ( for ex. 11 KV / 6.6KV two trfs but different vector groups can we parallelise both of them ,, what happens if we parallelise them

1 Answers  


What is creepage distance..... what will be the value for different voltage level

0 Answers  


We are installing a 1.6 MVA transformer at our crusher plant and the feeder of HPSEBL is 2 km away at substaion . and a VCB is installed in the substaion which is 2 km away from transformer so we need another VCB near the transformer.

2 Answers   SCPL,


what is surge voltage and surge current?

2 Answers   MES,


a 650 KVA diesel generator is 1500 rpm, voltage is 415V n full load amps is 805 something,when are applied load more than 400 amps it's voltage is dropping, what is the reasons...?

4 Answers  


If a fan get trip and run in reverse direction due to system flow. Now in this condition during starting how can a VFD bring this negative speed to zero and later run in forward direction?

2 Answers   Aditya Birla, Siemens,


the max. power will be transferred if …… a) sending end vol. is high b) receiving end v is high c)…….. d) corona loss is least

2 Answers   Engineers India Limited,


what is the size of cable for 15kw motor and 85 meter cable length using with vfd

0 Answers  


Why inductor short on dc and capacitor allow to flow ac?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)