How much sq,mm cable need for 800 amps load
Answers were Sorted based on User's Feedback
Answer / suresh.m
For 800A We Can Use 2R X 3.5CX300Sqmm.Al.Ar Cale But As Per
T.N.E.B We Should Use 3RX3.5CX 400Sq.mm Al.Ar.Cable.
Consider 1 Amp=1Sqmm For Aluminum Cable For Safety And
Starting Current We have to Consider 1.5 Times the Rated
Current that means 800*1.5=1200A
Is This Answer Correct ? | 10 Yes | 1 No |
Answer / parthasarathy
There is lot things we have an eye for choosing the cable selection for higher load.
Cable is of two types - copper and aluminium.
For aluminium cable at 800 amps load
We need to lay about 2Rx 400 square.mm Al. AR. Cable is enough ,more than we have an eye for how much length of the cable should lay.
For copper cable- 2Rx 240 square.mm copper flexible cable is enough.
Load is major constrain for cable laying and distance of cable also play a role.
Is This Answer Correct ? | 1 Yes | 0 No |
what is the technical diffrences of mccb and acb
what is the effect of leading power factor
3 Answers Aurobindo, R L Steels and Energy,
What is the permissible value of earth resistance and as per which standard / act / rule ?
directional relay is typically used to respond in fault condition who it can be used just as reverse power protection which purely senes direction reversal to operate a circuit breaker?
A 3PH MOTOR RUNNING IN NORMAL CONDITION AND ITS AMPERE ALSO UNDER ITS FULL LOAD CURRENT,ITS CABLE RATINGS ALSO HIGER THN ITS CAPACITY,BUT ITS CABLE GETTING ABNORMAL HEAT(NOT TOO HOT)WHY ITS GETTING HOT LIK THIS
What is meant by reset level of the relay?
Why indian power system in 11kv,22kv,33kv,66kv,110kv,220kv ? 2) Why ups required dedicated earth?
how can we calculate the current
how to modify DOL control panel into Delta Y connection?
What is the Maximum Power generation capacity of a Synchronus Machine ??
Please give me a ansver for why currant transforme noe point should erthing
induction 3 phase motor terminal connection