Dear All, Pls let me know about ELR.... CBCT is using for
singnal purpose... How it works.. any body can explain
pls.......
Answers were Sorted based on User's Feedback
Answer / gururaj dambal
ELR Earth Leakage Relays along with CBCT are used to detect
leakage current in the earhing. If the earthing is not
proper a small amount of current will appear (in the order
of mA). ELR will continuously monitor the leakage current
if it exceeds the set threshold an output electromechanical
relay (which is inside the ELR) will operate. The output
relay contact can be connected to circuite breakers /
contactor to isolate power supply or alarms.
CBCT Core Balance Current Transformers these will come in
different sizes. the core material will be either nickel or
alloy of nickel, copper wire will be wounded on the core
and properly insulated. The 3-phase line along with neutral
are passed in this core and secondary is connected to ELR.
Idealy the leakage current should be zero if any earth
leakage happen the leakage current will appear at CBCT
secondary it will be detected by ELR.
| Is This Answer Correct ? | 36 Yes | 3 No |
Answer / santosh
I agree with you. But exactly is the functionality of CBCT as compared to ELR, since ELR will be used to detect the leakage currents.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / s.murugan kumar
CBCT is used for current leakage purpose via earth.If any
leakage current goes to any equipments (For example:Busduct)
it will be by pass that the leakage current to earth.So it
will act some relay.This is the CBCT purpose.This is not a
signal purpose this is protection purpose of any equipments.
| Is This Answer Correct ? | 1 Yes | 2 No |
How generator NPS(NEGATIVE PHASE SEQUENCE TEST)TEST WAS DONE? PROCEDURE WITH DETAILS?
Why we find the sensitivity for the CT's to check?
Is single load(eg: three phase motor) having all the components like positive,negative,zero sequence components during fault condition?
What is CBCT ,why and whereit is used?
What is the method to calculate the capacitor bank rating for say 50 KW load and how do we connect each capacitor to busbar??
what is the grounding Calculation formula? spouse i want to provide grounding to 3phase 18kw motor or i want to provide ground to 3phase 10kva dry type transformere or you give me any exemple...... Thanks.
what happens if power factor is maintained at 0.9?give me the answer in technicall way rather than telling the penality n all
How to calculate cable size for a particular load? i have 12 MW,11KV Motor 3 Phase, what should be cablesize? What are the points to remember for cable sizing calculations?
I NEED RRB CHENNAI (JE ELECTRICAL) QUESTION PAPER FOR LAST 5 YEAR AND I NEED RRB (JE ELECTRICAL) SYLLABUS.PLEASE SEND MY E-MAIL joo28_eee@yahoo.co.in
12 Answers DFM, Hindustan Unilever Limited, JE, Pace, RRB,
how steam converted into electricity in power plant
What phase difference between p and s winding of transformer
how to calculate mf when meter and cTPT detail are given
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)