Can anyone explain how the vector diagram of a transformer
which doesn't have name plate be found whether it is
Dy11/Dy5/Yd11 and so on?
Answers were Sorted based on User's Feedback
Answer / geno peter
well , we can find the vector group by doing vector group
test
Is This Answer Correct ? | 13 Yes | 1 No |
Answer / loke
Ya ! first of all you can decide Yd or Dy by seeing it
primary & secondary connections and 1,2,3....11 we can
decide it by doing vector group tests int that we can check
phase shift of wave form & we can conclude
Is This Answer Correct ? | 7 Yes | 0 No |
Whether Dy or Yd can be ascertained from the bushings.To
find particular vector group ,CRO can be used finding
relationship between the current vectors.e.g.In Dy 11 I2R
lags I1R by 30 degrees Number 11 denotes position of minute-
hand in a clock.It can also found out by taking various
voltage measuremnts and analysing
Is This Answer Correct ? | 7 Yes | 0 No |
Yah! can.
If Dy11
Primary winding having only 3 terminals with high
resistance and secondary havign 4 terminals with low
resistance.
If Yd11
Primary having 4 terminals with high resistance and
secondary having 3 terminals with low resistance.
If Dy5
This is not a verctor group.
Eppdi???
Is This Answer Correct ? | 8 Yes | 30 No |
what is difference between ac1 and ac3 contactor and why it is needed to be selected?
A 100KVA SINGLE PHASE TRANSFORMER 10000/200V,50HZ REQUIRES 300V AT HV SIDE TO CIRCULATE FULL LOAD CURRENT WITH LV SHORT CIRCUITED.THE INTAKE IS 1000W.THE % OF REGULATION ON FULL LOAD AT 0.8 PF LAGGING WILL BE HOW MUCH AND THE SECONDARY TERMINAL VOLTAGE ON 0.8 PF LEADING WILL BE
What is APFC Panel????
if transformer winding burn on dc supply then why not alternator rotor winding please post answer on y.sakhare@rediffmail.com
What is the accepted limit to increase the choosen transformer capacity over the load and why ?
what is the formula to calculate the fault level current for any substation?
why do we provide metallic enclosure to bus duct and then ground it?
with out colour codeing on conductor how can be find what is r,what is b,what is y phases.....
A 40 kva transformer has a core loss of 400W and a full load copper loss of 800W. What is The proportion of full load at maxmimum efficiency?
HOW TO CALCULATE SINGLE PHASE AMPERES IN 3 PHASE TRANSFORMER? GIVE AN EXAMPLE PLZZZ
How can we find out LT UG cable fault (size,from-4*25mm sqr to 4*300mm sqr)? How mani types UG cable faults?
Why Lighting transformers are used? what will be the current if lightings connected through direct raw power?