Answer / suresh
diffrential relay used in generator for sense the winding
fualt
| Is This Answer Correct ? | 2 Yes | 0 No |
That works on difference of two current thats why known as
diffrential relay for example two cts one on generator
phase ct and other r on neutral side both cts passing for
example 5amps but the direction of current iz opposite so
the resultant iz zero that senses the relay if there is any
fault in the generator so the current increase on fault
side and the dirrence current increase and relay trip the
CB that iz the protection of generator transformer winding
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / musa
diffrential relay main protection for generator and
transformer ,between protection area not for outage short
circuit
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / ashish umrao
the diffrential relay used in which position when proctect
the specfice jone like feeder ,tranfromer ,bus bar,has a not
fluctuate the voltage .but generator has a variable load so
voltage are up and down so dose not use the this relay.
| Is This Answer Correct ? | 1 Yes | 7 No |
We have AC-transformer 110/13.8kv,40MVA.If DC-Voltage=110kv is applied in its primary what will happen?
What is the difference between single point and double point bonding. please kindly detail about bonding of cables.
what to do with nuetral when Generators are running in parrellel
what is the IEC standard for Power Cable installation in onshore (like in direct buried ground or above groung)
how to calculate circuit breaker capacity
What is the mechanism of WTI
What is cable gland,why does use for?
What size cable is used for HT cable to the transformer of 630kVA, and the supply voltage is 11kV
IN 6.6KV 3 phase switch gear .i will give 6.6kv to R phase only to earth in during H.v testing (through H.v KIT).what happen remaining phases.how much voltage get remaining phases.why? explain.
Terminal blocks is used for segregate the connections... There is any principle for terminal block..?
how we done power management?
why we are connecting the alternator to a steam turbine of higher RPM then the rated RPM of alternator? For example:( connecting 1500 rpm alternator to 7600 rpm steam turbine). we can directly connect the same rpm turbine to alternator know??? is there any special reason ???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)