can we replace a pressure transmitter of range 0 to 25
Kg/cm2 by a Pressure transmitter of range 0 to 10
Kg/cm2 ?.. Will it affect 4 to 20 mA output signal which we
will feed to the PLC.

Answers were Sorted based on User's Feedback



can we replace a pressure transmitter of range 0 to 25 Kg/cm2 by a Pressure transmitter of range 0..

Answer / ruchita

Yes it will affect the 4-20 mA signal. say for example if we are using PT of rsnge 0 to 25 bar bt internally we use only 0 to 10 bar range den it can be replaced otherwise not

Is This Answer Correct ?    9 Yes 4 No

can we replace a pressure transmitter of range 0 to 25 Kg/cm2 by a Pressure transmitter of range 0..

Answer / yashwant

yes, only make sure the pressure will never rise beyond 10 I
think its design for 25 in safety condition. if u wish O/p in
0-10 you can scale 4-20 ma as 0-10 at plc, no need to change
tx.

Is This Answer Correct ?    5 Yes 0 No

can we replace a pressure transmitter of range 0 to 25 Kg/cm2 by a Pressure transmitter of range 0..

Answer / vijay

it depend upon ur range in the application for example
piston producing pressure within 10kg/cm2 then u can use it
by change program in the plc otherwise u cant

Is This Answer Correct ?    5 Yes 3 No

can we replace a pressure transmitter of range 0 to 25 Kg/cm2 by a Pressure transmitter of range 0..

Answer / vinod hepat

Yes first of all note whether range is suitable for ur
application.replace transmitter & accordingly change the
range in DCS.

Is This Answer Correct ?    2 Yes 0 No

can we replace a pressure transmitter of range 0 to 25 Kg/cm2 by a Pressure transmitter of range 0..

Answer / madhav kamble

Yes. you can replace the pressure transmitter form 0-25 to
0-10. it willnot change the 4-20 mA which we will send to
the PLC but you to change the calibration at PLC for New
0-10 transmitter.

Is This Answer Correct ?    2 Yes 1 No

can we replace a pressure transmitter of range 0 to 25 Kg/cm2 by a Pressure transmitter of range 0..

Answer / govind singh

Going by standards, 20 mA of first transmitter will read 25 kg/cm2 pressure, while same reading for second transmitter will be 10 kg/cm2. So at same pressure, both transmitters will send different current signals. So calibration at the DCS end will be needed.

Is This Answer Correct ?    1 Yes 0 No

can we replace a pressure transmitter of range 0 to 25 Kg/cm2 by a Pressure transmitter of range 0..

Answer / imran

first of all you need permission to replace pressure tx
from operation instead 0-25 by swaping 0-10cause it will
effect process & may you r going to upset process other
point of view by technical you need to configure it & it
will give you output vice varsa

Is This Answer Correct ?    2 Yes 3 No

can we replace a pressure transmitter of range 0 to 25 Kg/cm2 by a Pressure transmitter of range 0..

Answer / dinesh kumar

Its not possible by answering without knowing the application

But in both the cases v can get the 4-20mA output

In case if the o/p doesnt goes beyond 10kg then v can replace and the o/p side of tx shud be calibrated before installing and the changes shud be entered on plc.

In another case if the user wants better accuracy he may b using 0-25kg/cm2 tx eventhough the internal pressure is b/w 0-10kg/cm2

Is This Answer Correct ?    0 Yes 1 No

can we replace a pressure transmitter of range 0 to 25 Kg/cm2 by a Pressure transmitter of range 0..

Answer / trideep

If range is in b/w 0-10 kg/cm2 or with in that, then it will do..

Is This Answer Correct ?    0 Yes 3 No

Post New Answer

More Instrumentation Interview Questions

Why all the drains(Gland sealing,ESV,Casing inlet etc) are directly connected to the flash tank instead of hotwell of the condensor in the power plant? My Email Id:naba02222@gmail.com

0 Answers   ABB, Jindal,


Which standard of hazardous area classification used in India?

1 Answers   Orchid,


OBJECTIVE TYPE QUESTIONS OF ANALYTICAL INSTRUMENTATION

0 Answers   Fauji Fertilizer, GSECL, NFL, Power Plant,


As an industrial instrument technician what we have to know?

3 Answers  


what are the three main programming languages in plc

12 Answers  






What is the difference between PLC and DCS?

3 Answers  


what happens when the profibus fails while in operation (operation of a valve)?

5 Answers   L&T,


what is the meaning of Domain server?

2 Answers  


How digital input and digital output 's are working in dcs

0 Answers   BBV, Indiabulls,


can anyone tel the syllabus or previous year question paper for BHAVINI(EIE)2014.

0 Answers   Bhavini,


What is the purpose of LO Overhead tank in turbines.

0 Answers   ADMA OPCO,


i have 80cm water tank.how can i use DPT as level mesurment.pls give specs for that..? We have air comp.from that moisture comeout to one tank.i want to mesure level of water in that tank and then after operat one sov to dicharge water after high level.

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)