in the construction field why hook up s.s.tubing for
transmitter using upto 6mtrs of closed loop, but y not
open loop nomore restriction
Answers were Sorted based on User's Feedback
Answer / s
Hook-up Diagram having installation details like
vaves,tee,elbow sizes.It is a detailed diagram for
Particular equipment installation which is not available in
P&ID.
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / chepin
S answer is right. Could some one pls share sample of the
hook up drawing.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / www.islamqa.com
I think it's related to system response time, 6 meters
limitation to make the feedback pressure signal built up
through the pipeline and arrive to I/P or controller in
suitable time.
open loop has no feedback so there's no limitations.
Regards,
Ahmed Sabry
Control and Instrumentation Engineer
GPC - General Petroleum Company
ahmedsabry.online@gmail.com
CELL.: 00 2 0121367310
Is This Answer Correct ? | 0 Yes | 0 No |
Dear Friends, we are planning to design Power distribution and Fiber optic in the same cabinet.Like Front side Fiber optic and Rear side Power distribution.Is it any possibility of problem occurs like interference etc? Your answer is highly appreciate.
what is LAS in foundation fieldbus protocol?
what is IPS (instrument protective system)?
what do u mean by compensation n pid tunning?in pid tunning what you tunned?is it possible 2 tune p i d
If a normal magnetic type flow transmitter that can measure flow, temperature and show this parameters on field, is it possible by any means to get this (flow and temperature) parameters info. On dcs? And if yes then with HART, FO communication or any other communication system?
1 Answers Process Control Technologies,
different between calibration range and instrument range ?
what is the difference between active & reactive power?
What is the standard height for stancion supports?
what is Least Value of MICROMETER?
In separator VFD frequently trip with OVER VOLTAGE Fault What is the reason?
why 1 to 5 vdc is used for output measurment
What is voltage regulator?