in the construction field why hook up s.s.tubing for
transmitter using upto 6mtrs of closed loop, but y not
open loop nomore restriction
Answers were Sorted based on User's Feedback
Answer / s
Hook-up Diagram having installation details like
vaves,tee,elbow sizes.It is a detailed diagram for
Particular equipment installation which is not available in
P&ID.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / chepin
S answer is right. Could some one pls share sample of the
hook up drawing.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / www.islamqa.com
I think it's related to system response time, 6 meters
limitation to make the feedback pressure signal built up
through the pipeline and arrive to I/P or controller in
suitable time.
open loop has no feedback so there's no limitations.
Regards,
Ahmed Sabry
Control and Instrumentation Engineer
GPC - General Petroleum Company
ahmedsabry.online@gmail.com
CELL.: 00 2 0121367310
| Is This Answer Correct ? | 0 Yes | 0 No |
what is Analog input/output & Digital input/output,
2 Answers Bapco Bahrain Petroleum Company,
how to calibrate level transmitter
what are the types of a thermocouple
While giving Power Supply of 24 VDC to a Transmitter,why Shield Terminal is connected either at Transmitter or at ISB.Why not Shield Terminal connected at both ends.If the Reason is to avoid Noise interference,which type of noice that is interfering.Is the Noice from the 24 VDC supply terminals or from any external source.
Dear Friends, we are planning to design Power distribution and Fiber optic in the same cabinet.Like Front side Fiber optic and Rear side Power distribution.Is it any possibility of problem occurs like interference etc? Your answer is highly appreciate.
yogokowa field bus system transmitter all's we are geting IOP fault in Contiunes please help me fine how we can normal the broblems?
how to check control valve was passing?how to check online?
In separator VFD frequently trip with OVER VOLTAGE Fault What is the reason?
-200mmwc to 500mmwc range transmitter have there 4mA is -200 and 20mA is 500.what is the range in 12mA?
what are the values of fuel flow rate in various places in boiler.
Profibus DP is a multi-master system. Would it work on RS-485 4W or not, and justify your answer
Is there any relation between Artificial Intelligence and Instrumentation?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)