WE ARE HAVING YOKOGAWA CENTUM CS 3000 DCS, 2 FCS AND 4 HIS "
When the operation Download to HIS message appears:
Equalize start. HIS0163
WARNING: Could not connect to equalize destination. (7001)
Retrying. Number of retries = 0/1
ERROR: LdXopsLoadMain: connect error 10060
ERROR: LdXopsLoadMain: connect error 10060
ERROR: Processing terminated due to connection error. (7002)
Equalization end with errors. HIS0163
---- ERROR = 3 WARNING = 1 ----

Tell me, please, why and how to solve the problem."

Answers were Sorted based on User's Feedback



WE ARE HAVING YOKOGAWA CENTUM CS 3000 DCS, 2 FCS AND 4 HIS " When the operation Download to HI..

Answer / jigaranadkat

Dear Prasanth,

Please rest assured that your control network is good you
only have the problem in your open network. Thats the
reason that your plant functionality will not be affcted
but you can not download in to HIS0163.

Please follow the below procedure and let me know the
feedback...

1) Check the IP address of HIS0163. It should be :
172.17.01.63 and subnet mask : 255.255.0.0
2) Check for corruption of ethernet driver : (Right click
on my computer---> Go to device manager---> Check for
ethernet driver corruption).
3) Go to run.... Type CMD and give folling command...
ping 172.17.01.63... You should not face any dropped
package.
4) Go to run and type: \\172.17.01.63 or \\his0163
You should be exposed to common shared folder CS1000
5) Disable firewall in HIS0163.

7001/7002 is the code that your ENG STATION is not able to
find HIS0163 in the network.

* As a default setting, due to some group policy setting ..
Connection with blank password will be denied access. So
try to have a common administrative password for HIS0164
and HIS0163 and for operator USER NAME=CENTUM and PASSWORD=
CENTUM.

You may write your feedback to

anadkat.jigar@gmail.com

Hope this will resolve your problem.

Thanks & Regards,

Jigar Anadkat
Instrument Engineer
IBN RUSHD a SABIC affiliate.

Is This Answer Correct ?    11 Yes 0 No

WE ARE HAVING YOKOGAWA CENTUM CS 3000 DCS, 2 FCS AND 4 HIS " When the operation Download to HI..

Answer / prashanth

thanks mr Jigar Anadkat
Instrument Engineer
IBN RUSHD a SABIC affiliate.

your suggession really helped

actualy firewall was turned on in HIS0163.
I TURNED OFF the fire wall and gave download,then it got
dowloaded successfully.

thank you

Is This Answer Correct ?    1 Yes 0 No

WE ARE HAVING YOKOGAWA CENTUM CS 3000 DCS, 2 FCS AND 4 HIS " When the operation Download to HI..

Answer / karthik

This means that HIS0163 is down and not connected to the
control network. Check Vnet/IP BUS1 and BUS2 connections and
the IP setting.

Once it's rectified , you should find HIS0163 in .SO (System
status overview).

Is This Answer Correct ?    2 Yes 2 No

WE ARE HAVING YOKOGAWA CENTUM CS 3000 DCS, 2 FCS AND 4 HIS " When the operation Download to HI..

Answer / jaguirre

Dear Prashath,
Just found your solution here in this website.
Can I asked for other possible solutions. All 5 items you gave was checked and verified but still, i'm not able to equalize.

Thanks and hoping for any suggestions.

Regards,
John

Is This Answer Correct ?    1 Yes 1 No

WE ARE HAVING YOKOGAWA CENTUM CS 3000 DCS, 2 FCS AND 4 HIS " When the operation Download to HI..

Answer / jaguirre

Dear Jigar Anadkat / Prashath,

This is the error.

Equalize start. HIS1145
WARNING: Could not connect to equalize destination. (7001) Retrying. Number of retries = 0/1
ERROR: LdXopsLoadMain: connect error 10061
ERROR: Processing terminated due to connection error. (7002)
Equalization end with errors. HIS1145
---- ERROR = 2 WARNING = 1 ----

Regards,
John

Is This Answer Correct ?    1 Yes 1 No

WE ARE HAVING YOKOGAWA CENTUM CS 3000 DCS, 2 FCS AND 4 HIS " When the operation Download to HI..

Answer / sha

replace your vnet card

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

I have applied the post Junior Engineer-(TM)in R.R.B CHANDIGARH recently . what type of question i have to practice and which book ?. can i get any model question paper?

3 Answers   RRB,


what is AWG?

2 Answers   NTPC,


Why trim span ? How?

0 Answers  


What is NAMUR standard and why its allways reletad with Sollenoid

2 Answers  


Describe the function of Accumulator into the Pump

0 Answers  






1. What means HART communicator / where it is used / how to use it? 2. Types of Thermocouples and its temperature ranges / output of thermocouple? 3. Types of RTDs and its temperature ranges / output of RTD? 4. Idea about Temperature Transmitters? 5. Difference between Analog and Digital signals? 6. Difference between “2 wire” and “4 wire” system / instruments? 7. Difference between “Potential” and “Potential free” contact? 8. Types of flow meters / transmitters? 9. Types of level transmitters? 10. Difference between “Power/Control” cable and “Instrument” cable? 11. What means “shield” and “screen” in cables / how it is useful? 12. Draw a schematic of closed loop circuit of flow / level / pressure / temperature? 13. Idea about calibration of Control valve / positioned / I/P? 14. How to bypass a digital/analog signal in PLC/DCS by hardwire and software?

6 Answers   JSL,


What is controller? What is transmitter?

1 Answers  


How can we say that accuracy of measurement increases by using 3 or 4 wire RTD? because for example: If resistance of RTD element is say r ohms and Resistance of the cable from transmitter to RTD is R ohms And if 4 wire RTD is used, ____._____________________ R ohms | |_____._____________________ R ohms / \ / r ohms \ \ | |______.__________________ R Ohms | |_______._________________ R ohms Then the actual resistance measured will be: Total = r + R/2 + R/2 = r +R Ohms Note: r+R instead of r ohms. hence error

2 Answers  


Which type of diaphragm use in costic line, dm water line, natural gas line, oil line?

0 Answers  


please send the hpcl (instrumentation) model placement papers to my mail....

9 Answers   HPCL, Invensys, IOCL, ONGC,


how will you check torque value during Factory acceptance Test for control valve/ESD ON/OFF VALE how will you confirm this torque value is being correct, Which document will you be refer.

0 Answers  


Why the ammonia and Nitric Acid level indicators is with millimeter ? and What is the conversion form millimeters that level indicator indicate to weight ?

0 Answers   EHC,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)