WE ARE HAVING YOKOGAWA CENTUM CS 3000 DCS, 2 FCS AND 4 HIS "
When the operation Download to HIS message appears:
Equalize start. HIS0163
WARNING: Could not connect to equalize destination. (7001)
Retrying. Number of retries = 0/1
ERROR: LdXopsLoadMain: connect error 10060
ERROR: LdXopsLoadMain: connect error 10060
ERROR: Processing terminated due to connection error. (7002)
Equalization end with errors. HIS0163
---- ERROR = 3 WARNING = 1 ----
Tell me, please, why and how to solve the problem."
Answers were Sorted based on User's Feedback
Answer / jigaranadkat
Dear Prasanth,
Please rest assured that your control network is good you
only have the problem in your open network. Thats the
reason that your plant functionality will not be affcted
but you can not download in to HIS0163.
Please follow the below procedure and let me know the
feedback...
1) Check the IP address of HIS0163. It should be :
172.17.01.63 and subnet mask : 255.255.0.0
2) Check for corruption of ethernet driver : (Right click
on my computer---> Go to device manager---> Check for
ethernet driver corruption).
3) Go to run.... Type CMD and give folling command...
ping 172.17.01.63... You should not face any dropped
package.
4) Go to run and type: \\172.17.01.63 or \\his0163
You should be exposed to common shared folder CS1000
5) Disable firewall in HIS0163.
7001/7002 is the code that your ENG STATION is not able to
find HIS0163 in the network.
* As a default setting, due to some group policy setting ..
Connection with blank password will be denied access. So
try to have a common administrative password for HIS0164
and HIS0163 and for operator USER NAME=CENTUM and PASSWORD=
CENTUM.
You may write your feedback to
anadkat.jigar@gmail.com
Hope this will resolve your problem.
Thanks & Regards,
Jigar Anadkat
Instrument Engineer
IBN RUSHD a SABIC affiliate.
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / prashanth
thanks mr Jigar Anadkat
Instrument Engineer
IBN RUSHD a SABIC affiliate.
your suggession really helped
actualy firewall was turned on in HIS0163.
I TURNED OFF the fire wall and gave download,then it got
dowloaded successfully.
thank you
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / karthik
This means that HIS0163 is down and not connected to the
control network. Check Vnet/IP BUS1 and BUS2 connections and
the IP setting.
Once it's rectified , you should find HIS0163 in .SO (System
status overview).
| Is This Answer Correct ? | 2 Yes | 2 No |
Dear Jigar Anadkat / Prashath,
This is the error.
Equalize start. HIS1145
WARNING: Could not connect to equalize destination. (7001) Retrying. Number of retries = 0/1
ERROR: LdXopsLoadMain: connect error 10061
ERROR: Processing terminated due to connection error. (7002)
Equalization end with errors. HIS1145
---- ERROR = 2 WARNING = 1 ----
Regards,
John
| Is This Answer Correct ? | 1 Yes | 1 No |
Hi, I'd like to know the purpose of MOS (maintenance override switch). At site, these switches are installed in a stanchion with the transmitter (connected to ESD). thank you.
3 Answers Adani, Adani Wilmar,
what do you know about Foundation Fieldbus?
Which wiring connection is preferred in motor for industrial use?
generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?
why fuse block is not used for AI signal?
If we increase PI controller what will be action.
WHAT IS DIFFERANCE BETWEEN INSTRUMENT AND EQUIPMENT
Im having problems with interfase betwen SPI v7.0 and SPPID v5.05. Previous versions of Intools shoul be fixed with SPPIDproj.ocx file. It was necessary to replace this file with one that allows the connection between different versions of SPPID. It is necessary in the current version to do the same?Thanks
tion 0,50,100% equql to voltage formula?
We have a Yokogawa Micro-XL DCS, which is having around 300 I/O, but whenever there is any wire gets grounded in field, the 24v supply to all loops gets dipped & all the indications at DCS goes to IOP(shows input open), at present we have fixed 500mA fuses in all the lines but which does not working. Does it required to replace with lower amps fuse, then how much or is there any other solution for this.
I have seen the Temperature element (T/C & RTD) installed in process line on 45 degree position, Why? What it mean? How many types of tapping position for temperature elements?
How the sizing of the analog signal cable is calculate?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)