NGR used for limiting the ground fault cuurent that is
installed in between generator neutral point and earth in
case of fault that limit the fault current that is of
diffrent type resiatance type, reactance ,petrson coil
earthing. In case of one phase fault that NGR limit the
current and relays detect that and trips the generator.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sivashanmugam
neutral grounding resistor as like that of an earth ... in
generating station most probably transformer is an star to
delta connection generator side delta to star connection i
the transformer side grounding is not possible in case of
that ... one earthing transformer will be palced its an
zigzag winding for grounding the transformer side earth
bcos its an delta conn ... for neutral grounding resistor
ter will be an ngr panel in generator side unequal of
currents in phases grounded in ngr .... am not sure in this
answer if u peoples refer further mail me thank you.....
| Is This Answer Correct ? | 2 Yes | 3 No |
why transformer cannot rotate though the princplebehind induction motor is similar to a transformer?
why different series of vfds (like allenbradley)are used in industry ?
why we use condenser in the thermal power plant, althrough the same vapour will be again heated
what is the abbreviation for F.M In FM-200 fire suppression system
how to calculation increase power factor for single phase
Does power factor vary with speed?If yes, how?If not, why?
a 25kvar capacitor bank connected to the secondary side of transformer.then why the capacitor draws more current then rated
What is the diffrence between PS & metering CT (5p20,0.5 etc.)? Why in PS class CT only Vk is given ? Is PS class CT is more accurate than metering CT?
Voltage drop is the:(a) Maximum potential(b) Difference in potential between two points(c) Voltage at the end of a circuit(d) Voltage produced by a source
how the vaccum ckt breaker workes..? how the arc is quenching in it?
how to calculate the load on transformer..????
i will applied in 1U-1W on 440 volt primary delta side. what is the result of magtic balance test
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)