Answer / ashish
Any DG Require Four earthing strip Two For Neutral Earthing
& Two For Body Earthing.
Incase of 250 KVA DG 30X6 mm GI Earthing Strip is Suitable.
| Is This Answer Correct ? | 50 Yes | 24 No |
Answer / ajaydoss
Thanks for reply. I need the calculation (formula) .
| Is This Answer Correct ? | 29 Yes | 15 No |
Answer / ramesh p n
Voltage is the potential difference between two Conductors,
for Single Phase and the fro three phase system it is the
potential Difference between three phases and the neutral
for Example in india WE have 240 Volts A C Voltage for
single phase and 415 V for 3 Phase,
Forula to determine Power, Voltage and Currents
1 Phase : P = V X I = { Power(in watts)= Voltage X Current}
3 Phase P = rootof3 X V X I cos Phi,
Power = 1.732 X Voltage X current X Power Fator
| Is This Answer Correct ? | 17 Yes | 8 No |
THE RATED CURRENT OUTPUT WILLBE 434AMP AND THE EARTH
CONTINUITY CONDUCTOR SHOULD BE HALF OF THE LARGEST CURRENT
CARRYING CONDUCTOR.
IF THERE IS CU CONDUCTOR OF SIZE 400SQ. MM IS USED THEN
EARTH CONDUCTOR SHOULD BE 200 SQ. MM OF DIMENSION 40X6 CU
STRIP CAN WORK EFFECTIVELY.
| Is This Answer Correct ? | 14 Yes | 12 No |
Answer / anupam mahesh
Forula to determine Power, Voltage and Currents
1 Phase : P = V X I = { Power(in watts)= Voltage X Current}
3 Phase P = rootof3 X V X I cos Phi,
Power = 1.732 X Voltage X current X Power Fator
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / rsbangra
what is the voltage level ?
kva =1.732*v*i
i=kva/1.732*v
we get current value then find out current carring bus size
| Is This Answer Correct ? | 8 Yes | 8 No |
Answer / samson
Neutral will come in to picture whenever u start ur DG (
and not paralleing with a Grid as it will create a
circulating current), so worst thing that can happen is L.G
fault on a phase of generator or inside the winding , so
max current that can go is dg rating/ phase volatge ( use
formula above) so ur neutral should be capable of that
much curent ,( neglecting any contact resistance in ideal
case)
the switching of neutral is done through contactor.
use this to size strip
the I = K* A/ sqrt of time ( some of IS standered give u k
for bare conductor) Dg manufacturer will size support for
S.C forces
get k for alumi. or copper u can size to next standered
sizes available 20 x 6, 40 x5 n all
| Is This Answer Correct ? | 4 Yes | 5 No |
Answer / dg
Current should be 348Amp. As DG of 250KVA not 250Kw. So PF wont be used to calulate current.
| Is This Answer Correct ? | 4 Yes | 8 No |
In a panel 2500A ACB is the incoming breaker then what is the size of the bus bar?
For high frequency application we use which transformer?
what is the differnce between vector and phasor? are both same or there is difference between two term.?
How a Universal motor works in Both A.C and D.C? What is the constructional difference with other single phase motors?
what will happen when excitation of a synchronous machine is suddenly reduce to zero when it is running at full load..??
how to check a transformer insulation?
3 Answers Kirloskar, Kirloskar Chillers,
What are the different parts of Alternator and how it works?
which of the following loss varies with the load a)hystresis loss b)eddy current loss c)copper loss d)core loss
what are the stresses in circuit breakers ?
what is the magnitude of earthing and neutral voltage
how to select proper cable for ct wiring so that drop within the limit.
How to check 11000/1.732 to 110/1.732 Potentila transformer (PT)?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)