How to calculate earth flat size for 250 Kva DG and
transformer?
Answers were Sorted based on User's Feedback
Answer / ashish
Any DG Require Four earthing strip Two For Neutral Earthing
& Two For Body Earthing.
Incase of 250 KVA DG 30X6 mm GI Earthing Strip is Suitable.
| Is This Answer Correct ? | 50 Yes | 24 No |
Answer / ajaydoss
Thanks for reply. I need the calculation (formula) .
| Is This Answer Correct ? | 29 Yes | 15 No |
Answer / ramesh p n
Voltage is the potential difference between two Conductors,
for Single Phase and the fro three phase system it is the
potential Difference between three phases and the neutral
for Example in india WE have 240 Volts A C Voltage for
single phase and 415 V for 3 Phase,
Forula to determine Power, Voltage and Currents
1 Phase : P = V X I = { Power(in watts)= Voltage X Current}
3 Phase P = rootof3 X V X I cos Phi,
Power = 1.732 X Voltage X current X Power Fator
| Is This Answer Correct ? | 17 Yes | 8 No |
THE RATED CURRENT OUTPUT WILLBE 434AMP AND THE EARTH
CONTINUITY CONDUCTOR SHOULD BE HALF OF THE LARGEST CURRENT
CARRYING CONDUCTOR.
IF THERE IS CU CONDUCTOR OF SIZE 400SQ. MM IS USED THEN
EARTH CONDUCTOR SHOULD BE 200 SQ. MM OF DIMENSION 40X6 CU
STRIP CAN WORK EFFECTIVELY.
| Is This Answer Correct ? | 14 Yes | 12 No |
Answer / anupam mahesh
Forula to determine Power, Voltage and Currents
1 Phase : P = V X I = { Power(in watts)= Voltage X Current}
3 Phase P = rootof3 X V X I cos Phi,
Power = 1.732 X Voltage X current X Power Fator
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / rsbangra
what is the voltage level ?
kva =1.732*v*i
i=kva/1.732*v
we get current value then find out current carring bus size
| Is This Answer Correct ? | 8 Yes | 8 No |
Answer / samson
Neutral will come in to picture whenever u start ur DG (
and not paralleing with a Grid as it will create a
circulating current), so worst thing that can happen is L.G
fault on a phase of generator or inside the winding , so
max current that can go is dg rating/ phase volatge ( use
formula above) so ur neutral should be capable of that
much curent ,( neglecting any contact resistance in ideal
case)
the switching of neutral is done through contactor.
use this to size strip
the I = K* A/ sqrt of time ( some of IS standered give u k
for bare conductor) Dg manufacturer will size support for
S.C forces
get k for alumi. or copper u can size to next standered
sizes available 20 x 6, 40 x5 n all
| Is This Answer Correct ? | 4 Yes | 5 No |
Answer / dg
Current should be 348Amp. As DG of 250KVA not 250Kw. So PF wont be used to calulate current.
| Is This Answer Correct ? | 4 Yes | 8 No |
what is a universal motor? how it works?
is harmonic useful or it distort the alternating quantity?
what is the difference between surge arrestor and surge supressor
why we are grounding the neutral?
An 8 pole, 50 Hz, 3-phase IM is loaded to a poing where pull out torque will occur. The rotor resistance per phase is 0.3 ohm and motor stalls at 650 rpm. The rotor frequency at maximum torque point is A 3.33% B 4.44% C 5.55% D 6.66%
Why servomotor and induction motor are in different shape
How to check VFD outgoing voltage
What is systematic error?
what is TPN
Air circuit breaker safety
ho can we calculate the conductor insulation value according to their ratings like voltage,current etc.how insulation value related with voltage,current and power of amachine
what is VFD and where is use of it
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)