How to calculate earth flat size for 250 Kva DG and
transformer?

Answers were Sorted based on User's Feedback



How to calculate earth flat size for 250 Kva DG and transformer?..

Answer / ashish

Any DG Require Four earthing strip Two For Neutral Earthing
& Two For Body Earthing.
Incase of 250 KVA DG 30X6 mm GI Earthing Strip is Suitable.

Is This Answer Correct ?    50 Yes 24 No

How to calculate earth flat size for 250 Kva DG and transformer?..

Answer / ajaydoss

Thanks for reply. I need the calculation (formula) .

Is This Answer Correct ?    29 Yes 15 No

How to calculate earth flat size for 250 Kva DG and transformer?..

Answer / ramesh p n

Voltage is the potential difference between two Conductors,
for Single Phase and the fro three phase system it is the
potential Difference between three phases and the neutral
for Example in india WE have 240 Volts A C Voltage for
single phase and 415 V for 3 Phase,

Forula to determine Power, Voltage and Currents

1 Phase : P = V X I = { Power(in watts)= Voltage X Current}


3 Phase P = rootof3 X V X I cos Phi,


Power = 1.732 X Voltage X current X Power Fator

Is This Answer Correct ?    17 Yes 8 No

How to calculate earth flat size for 250 Kva DG and transformer?..

Answer / uma sanker dwivedi

THE RATED CURRENT OUTPUT WILLBE 434AMP AND THE EARTH
CONTINUITY CONDUCTOR SHOULD BE HALF OF THE LARGEST CURRENT
CARRYING CONDUCTOR.
IF THERE IS CU CONDUCTOR OF SIZE 400SQ. MM IS USED THEN
EARTH CONDUCTOR SHOULD BE 200 SQ. MM OF DIMENSION 40X6 CU
STRIP CAN WORK EFFECTIVELY.

Is This Answer Correct ?    14 Yes 12 No

How to calculate earth flat size for 250 Kva DG and transformer?..

Answer / anupam mahesh

Forula to determine Power, Voltage and Currents

1 Phase : P = V X I = { Power(in watts)= Voltage X Current}


3 Phase P = rootof3 X V X I cos Phi,


Power = 1.732 X Voltage X current X Power Fator

Is This Answer Correct ?    3 Yes 2 No

How to calculate earth flat size for 250 Kva DG and transformer?..

Answer / rsbangra

what is the voltage level ?
kva =1.732*v*i
i=kva/1.732*v

we get current value then find out current carring bus size

Is This Answer Correct ?    8 Yes 8 No

How to calculate earth flat size for 250 Kva DG and transformer?..

Answer / samson

Neutral will come in to picture whenever u start ur DG (
and not paralleing with a Grid as it will create a
circulating current), so worst thing that can happen is L.G
fault on a phase of generator or inside the winding , so
max current that can go is dg rating/ phase volatge ( use
formula above) so ur neutral should be capable of that
much curent ,( neglecting any contact resistance in ideal
case)

the switching of neutral is done through contactor.

use this to size strip
the I = K* A/ sqrt of time ( some of IS standered give u k
for bare conductor) Dg manufacturer will size support for
S.C forces

get k for alumi. or copper u can size to next standered
sizes available 20 x 6, 40 x5 n all

Is This Answer Correct ?    4 Yes 5 No

How to calculate earth flat size for 250 Kva DG and transformer?..

Answer / dg

Current should be 348Amp. As DG of 250KVA not 250Kw. So PF wont be used to calulate current.

Is This Answer Correct ?    4 Yes 8 No

Post New Answer

More Electrical Engineering Interview Questions

What is transient Phenomenon?

0 Answers  


What are steps to be taken while designing of DYN11 distribution transformer to achieve magnetising balance?

0 Answers  


Why generally the Rating of Transformers are in additions of 11 i.e. 11 kVA, 22 kVa, 33 kVA, etc........

8 Answers  


WHAT WILL HAPPEN IF INPUT SUPPLY OF RCBO IS CONNECTED TO OUTPUT SIDE

2 Answers   ABG Shipyard,


what is the 2MVA distribution transformer efficiency

1 Answers  






how to calculate the capacitor to maintain power factor?

0 Answers   Bosch,


Relation in between KWH & KVAH for Electrical consumption unit & how we can relate if KWH is lower than KVAH

11 Answers   Deepak Fertilisers, Torrent Pharma,


Reduction in supply voltage by 10% will change the torque of the motor by ___.

1 Answers   UGVCL Uttar Gujarat Vij Company Ltd,


why contactor not provided between output of VFD and motor?

6 Answers   Siemens,


what happend if the protection ct is by mistake put instead of measuring ct & vice versa?

2 Answers  


i have old tape recorder speakers(analog).nw i want to use it for my computer system.can i use it to my computer systeno m by using digital to analog converter??? what changes should i do in the system????

0 Answers  


how to select battery for 15 KVA UPS with formula

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)