hello dear
i have faced problem in drum level transmitter.
the problem is when i engrize the meter meter shows 100%
but the actual level 40 or something plz suggest me

Answers were Sorted based on User's Feedback



hello dear i have faced problem in drum level transmitter. the problem is when i engrize the mete..

Answer / aftab ahmed mazari

It seems that transmitter low side leg is leaking, or low
side is not being fully condensing.
Please chck low leg fittings, connections and if ok. Then
check transmitter high side and low side pressures with the
help of digital pressure gauge. May be transmitter low side
any problem.When you calibrate tranmitter workshop, also
apply pressure to its low side, indication should go down
to confirm that low side is ok.

aftabmazari@yahoo.com

Is This Answer Correct ?    1 Yes 0 No

hello dear i have faced problem in drum level transmitter. the problem is when i engrize the mete..

Answer / ikraamh5

plz give me answer

Is This Answer Correct ?    2 Yes 2 No

hello dear i have faced problem in drum level transmitter. the problem is when i engrize the mete..

Answer / s.arunraja

Please give me the Transmitter Calibration Range

Is This Answer Correct ?    0 Yes 0 No

hello dear i have faced problem in drum level transmitter. the problem is when i engrize the mete..

Answer / yomama

The impulse tubes must be filled with process fluid or fill
fluid such as glycol. Additionally the specific gravity of
the fill fluid must be calculated in reference to the
process fluid being measured

Glycerin (Specific Gravity=1.26) for the impulse tubes a
correction must be made.

DP span of 100”= physical height difference of impulse tubes
on vessel

SG of fluid being measured (Oil = 0.68)

Glycerin filled tubes (SG = 1.26)

Since the Low Pressure Leg will be filled with Glycerin we
multiply the span by the SG of the Fill Fluid

100” x 1.26 = 126” so the Lower Range value will be -126”
Span will be the LRV – (SG of fluid) x ( tank Level span) = 68”

-126” + 68” = -58”
-126 LRV
-58 URV

Is This Answer Correct ?    0 Yes 0 No

hello dear i have faced problem in drum level transmitter. the problem is when i engrize the mete..

Answer / yomama

The impulse tubes must be filled with process fluid or fill
fluid such as glycol. Additionally the specific gravity of
the fill fluid must be calculated in reference to the
process fluid being measured

Glycerin (Specific Gravity=1.26) for the impulse tubes a
correction must be made.

DP span of 100”= physical height difference of impulse tubes
on vessel

SG of fluid being measured (Oil = 0.68)

Glycerin filled tubes (SG = 1.26)

Since the Low Pressure Leg will be filled with Glycerin we
multiply the span by the SG of the Fill Fluid

100” x 1.26 = 126” so the Lower Range value will be -126”
Span will be the LRV – (SG of fluid) x ( tank Level span) = 68”

-126” + 68” = -58”
-126 LRV
-58 URV

Is This Answer Correct ?    0 Yes 0 No

hello dear i have faced problem in drum level transmitter. the problem is when i engrize the mete..

Answer / anwer

an instrument calibration range should be 60-80% and another
condition is range shall be more than max value.

Is This Answer Correct ?    0 Yes 0 No

hello dear i have faced problem in drum level transmitter. the problem is when i engrize the mete..

Answer / kakhlaq

re-check the transmitter range, process connections, if
this arrangement is wet leg type then check that the leg is
filled with liquid.

Is This Answer Correct ?    0 Yes 2 No

Post New Answer

More Instrumentation Interview Questions

What is the main three inputs of DCS?

1 Answers  


What is an SCR?

4 Answers   GAIL,


For 150 mtr cable run from DCS panel to transmitter (24 VDC with 4-20 ma output), need cable size. 1.5 sqmm is suitable?

2 Answers   NA,


what should be the attitude while answering an interviewer?

2 Answers  


what r all the closed loop used in boiler? for this related tell some web address..

3 Answers  






line up procedure for dp type flow transmitter?

0 Answers  


What is the difference b/w EMF, voltage & potential difference?

1 Answers  


how to calibrate a control valve?

7 Answers   Reliance, Telecon Systems,


What is principle of ultrasonic level transmitter?

3 Answers  


Why 4ma - 20ma signal used in instrumentation??

5 Answers  


open tank and close tank leavel transmiter about range and calibration

0 Answers  


how can I install "operating system " in may HART communicator? It is damaged, and it doesn't boot up.

1 Answers   ARPC,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)