1)how can calibrate temperature transmitter?
2)how can calibrate flow transmitter?
3)how can calibrate level transmitter?
Answers were Sorted based on User's Feedback
Answer / tontoy
1 prepare the instruments needed in calibrating temp.
transmetter.
2 unsrew the resistance input of the transmetter, and
connect it to a resistance box.
3. unsrew the output side of the transmetter, connect the
ammeter serries with the supply of 24 volts dc.
4. supply it with the resistance of 0% or 100 Ohm until
100%. and record it to the data in the as found.
5. the next is the zeroing. supply the input with 100ohm
resistance. adjust the adjustment of the zero side by
twisting slowly to the left to have an output of 4mA.
6. span- supply the transmitter with 100% depends on the
value of high temperature of the RTD value. and adjust it
to 20mA.
7 repeat it up to 4-5 times.
then supply is again with 100Ohn, mast have an output of
4mA until 100%.
record it to the data as asleft.
for 0% must have an output of 4mA, 25% 8mA, 50% 12mA, 75%
16Ma, and 20mA for 100%.
| Is This Answer Correct ? | 101 Yes | 17 No |
Answer / sumit yadav
1)There is equipment available where we can put RTD and
give temperature.Now set temp transmitter parameters to
produce mA equivalent to temp given.
| Is This Answer Correct ? | 71 Yes | 26 No |
Answer / gcs
1. First select the calibrating equipment
2. for ex: For RTD, select RTD circuit with zero and span adjustment potentiometers.
3. make the input quantity (temperature) to zero.
4. adjust the zero adjustment pot ntill the output of the RTD becomes zero.
5. make the input quantity to high (Ex.100 deg) and adjust the span pot till the output becomes 100.
6. Repeat steps 3 through 5 till there are no changes in zero and span pot.
7. now the instrument is calibrated.
| Is This Answer Correct ? | 13 Yes | 22 No |
An engineering term STALL used in compressor operation what it means?
Witch type cable use for rtd ,why?
1. For Steam drum level signal, why do we compensate with drum pressure signal? 2.For main steam Flow signal is comensated with main steam temperature signal and main steam pressure signal why?
please tel me the calibration of pneumatic controler.
If a control valve is hunting means means if we are giving 50% to the cv, the cv will open at 51% then slowly slwoly it will reaches 49% , so what to do for solve this problem. The cv is double acting and mounted for anti surge operation, it having 4 nos. volume booster, one sov, one positioner, etc..?
plz you help about Que paper of mahagenco previous your,any model paper relad to it{maharastra power genration}
How to convert mmWc(mili meter water colam) to tph(ton per hour)?
I have 475 hart communicator. this is not support any new type of instruments such as tranmitter,fieldvue DVC6200.DVC 200 since i got point out need to upgrade . my questions is how can upgrade new instruments software in my 475 hart communicator. can any answerplease>?
i have one tank of 500mm height, which is in under vacuum of 735 mmHg, I want measure level of the same using DPT , SO WHAT WILL BE THE URV & LRV, DENSITY OF THE TANK FLUID IS 0.95. is there necessary to fill the LP side with fluid.
WHEN BOTH WIRES OF THERMOCOUPLE R SHORTED WHAT IS THE OUTPUT THE TEMP ARE 0,30,250,320
what is the reset offset and control system in instrumentation
Why is it necessary to use compensation leg to measure the liquid level in a closed or pressurized tank?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)