how to measure temperature from resistance of rtd?and how to
measure temp from voltage of thermocouple?is there any formulas?
Answers were Sorted based on User's Feedback
Temperature measurement.
With RTD:
The Material used Is Platinum Which is very Sensitive to
the temperature as the temperature Changes the Resistance
changes.Which is next connected to form a Weatstone bridge
in the transmitter then According to the formula
R1/R2=R3/R4 since R2,R3,R4 are Constant So Change in RTD
Resistance R1 The Corresponding mA Signal is Obtained
through the transmitter to the system in control room.
With T/C:
Were As T/C is the Formation of two diffrent Material
Combined to form a T/C(SEEBACK EFFECT)As they r two
different materials Change in temperature Causes the change
in EMF generation between the two materials,This mV Signal
is then Transmitted to Marshelling cabinet to Convert it
into V because all Digital Signal read minimum 5V,it is
Converted by OP-Amp with 250ohm Resistance Across it whict
is convinient to DCS to read it.
| Is This Answer Correct ? | 7 Yes | 5 No |
Answer / nishat
to measure temperature through RTD there is a formula T=(R-100)/.385
FOR PLATINUM RTD rise in 1 degree there is increase of 0.385ohm resistance
about T/C IF ANYONE KNOW SO PLEASE DO ANSWER
| Is This Answer Correct ? | 0 Yes | 0 No |
During the measurement of Temperature from RTD, we have to
just disconnect the RTD from the control room,(as it is
externally powered, in case of thermocouple it is self
powered transducer) after disconnecting just measure
resistance of element e.g. 115 ohms.. then deduct 100 from
it...you will get say 15,,,then multiply this by 2.5..you
will get the temperature ,,approximately you will get 38
degrees..
| Is This Answer Correct ? | 0 Yes | 4 No |
can anyone tell free downloads website for fundamentals and principle of basic pressur,temperature,level and flow
What is the difference between Pressure Safety Valve and Pressure Relieve Valve, in what condition we prefer choose Pressure Safety Valve rather than Pressure Relieve Valve? and vice versa
we have LPG spherical Tank and we want to install DP Xmtr for level measurement.below are the physical measurements Total height of tank is 1850 mtr but 0% level is 1000mm above bottom and 100% level is 450 below upper side.What is the LRV and URV and please mention the formula .The SG of LPG is 0.53 and Wet Leg method will be used.
How would you choose differential range?
what is the diffrene between DCS System and PLC System
Isometric drawings are generated during _________________ phase of a project
Hi, am aniket, I got engineering degree in instrumentation and control, but as their were no job availabilities for engineer's post I started working as instrumentation technician I kuwait, so my question is is this technician's experience worth for getting the position of engineer?
1 Answers Almeer Technical Services,
how can i communicate with non-national instruments device with pc via labVIEW8.2
3 Answers Google, Mico, National Instruments,
how to calibrate displacer type level transmitter by dry weight method please mention formula for weight calculation
how u meassure a room temp?in rtd or themo couple?
What is transducer
I WANT SECURITY PAPER MILL, HOSHANGABAD TEST PAPER.KINDLY SEND TO MY MAIL ID
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)