avr is an automayic voltage regulator ... it regulates
voltage before it synchronise with grid after
synchronisation it regulates power factor why....

Answers were Sorted based on User's Feedback



avr is an automayic voltage regulator ... it regulates voltage before it synchronise with grid a..

Answer / k.prakashchandra

AVR maintains the set voltage and does not regulate it.APF
mode is an option in Auto- channel in addition to AVR mode
and it is put in action after synchronization.

Is This Answer Correct ?    1 Yes 0 No

avr is an automayic voltage regulator ... it regulates voltage before it synchronise with grid a..

Answer / k.prakashchandra

After synch,AVR keeps the gen voltage constant at the set
value. If the grid voltage is more than the gen voltage, the
pf becomes leading and lagging if the grid voltage is less
than the gen voltage.Then, in AVR mode the operator has to
reset the gen voltage so that the pf is slightly lagging.In
APF mode ,the pf always remains at the set value
irrespective of variations in grid voltage.

Is This Answer Correct ?    1 Yes 0 No

avr is an automayic voltage regulator ... it regulates voltage before it synchronise with grid a..

Answer / mohammed sajid

I can't understand your language mr.prakash,just explain
what is the function of AVR before & after synchronisation
with grid.

Is This Answer Correct ?    0 Yes 0 No

avr is an automayic voltage regulator ... it regulates voltage before it synchronise with grid a..

Answer / balu

Once the generator connects with the grid the system voltage depends upon to the grid referrence.the active power varies depends on the load.so load varies mean time reactive power also variey.so avr will maintaine power factor after synchronization.

Is This Answer Correct ?    0 Yes 0 No

avr is an automayic voltage regulator ... it regulates voltage before it synchronise with grid a..

Answer / k.prakashchandra

It is possible to have the changeover from AVR to APF mode
automatically on synchronization / closing unit CB and the
vice versa, using auxiliary switch of the breaker.

Is This Answer Correct ?    0 Yes 0 No

avr is an automayic voltage regulator ... it regulates voltage before it synchronise with grid a..

Answer / k.prakashchandra

It keeps the gen voltage the same at the set value
irrespective of variation in speed , load and grid voltage
after synchronization. It is useful whenever there is grid
failure as the gen speed suddenly increases to an extent
depending on the load interrupted.Then AVR does not allow
for rise in voltage.It is also very helpful while
synchronizing as you do not have to vary the excitation
every now and then ,once you have matched the voltages.If
you desire to keep the pf constant after synch and loading
,you have to switch over to APF mode from AVR ,both being
available with Auto channel.

Is This Answer Correct ?    0 Yes 0 No

avr is an automayic voltage regulator ... it regulates voltage before it synchronise with grid a..

Answer / it might be for easy calculati

It might be for
easy
calculation:-)

Is This Answer Correct ?    2 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

1. How many types of mangers? 2.How many types of capacitors? 3.pls tell me normally types alternator problems?

0 Answers   APCPDCL, Voith,


What the methode get earth resistance?

2 Answers  


why the NGR (neutral grounding resistor) always OFF during DG off?

0 Answers   Bhel,


why only 11kv level is used for transmission purpose? why not 230v?

7 Answers  


How can you test the vector group of power transformers?

2 Answers  






In Power transformer oil temperature or winding temperature will be high

3 Answers  


can anyone help me regarding bout Electrical designs and calculations .. which text book should i follow as i am a trainee engineer.Description of my work which is Electrical designs like cable sizing, lighting, lightning, Gensets sizing, motor sizing, transformer sizing, generator sizing, circuit breakers, PDB MCC PCC SLDB MLDB panels, Single line diagrams mainly, substation desings, cable routing and layouts, reactive power compensations, power factor improvement, voltage drop calculations, power generations, power transmission, power distributions all calculations.Please help me

3 Answers  


how LT meggar works

1 Answers   Essar,


can a motor acts as a generator

8 Answers   Cummins,


Pl. brief about break-down maintenance of machine tool.

0 Answers  


What is the meaning of CT 40/5, 100/5 or in HT lines 100/1 ????????

3 Answers   Amex,


WHY 6.6KV MOTORS ARE STAR CONNECTED AND WHY NOT DELTA CONNECTED,

15 Answers   Bhel,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)