avr is an automayic voltage regulator ... it regulates
voltage before it synchronise with grid after
synchronisation it regulates power factor why....
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
AVR maintains the set voltage and does not regulate it.APF
mode is an option in Auto- channel in addition to AVR mode
and it is put in action after synchronization.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
After synch,AVR keeps the gen voltage constant at the set
value. If the grid voltage is more than the gen voltage, the
pf becomes leading and lagging if the grid voltage is less
than the gen voltage.Then, in AVR mode the operator has to
reset the gen voltage so that the pf is slightly lagging.In
APF mode ,the pf always remains at the set value
irrespective of variations in grid voltage.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mohammed sajid
I can't understand your language mr.prakash,just explain
what is the function of AVR before & after synchronisation
with grid.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / balu
Once the generator connects with the grid the system voltage depends upon to the grid referrence.the active power varies depends on the load.so load varies mean time reactive power also variey.so avr will maintaine power factor after synchronization.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
It is possible to have the changeover from AVR to APF mode
automatically on synchronization / closing unit CB and the
vice versa, using auxiliary switch of the breaker.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
It keeps the gen voltage the same at the set value
irrespective of variation in speed , load and grid voltage
after synchronization. It is useful whenever there is grid
failure as the gen speed suddenly increases to an extent
depending on the load interrupted.Then AVR does not allow
for rise in voltage.It is also very helpful while
synchronizing as you do not have to vary the excitation
every now and then ,once you have matched the voltages.If
you desire to keep the pf constant after synch and loading
,you have to switch over to APF mode from AVR ,both being
available with Auto channel.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / it might be for easy calculati
It might be for
easy
calculation:-)
| Is This Answer Correct ? | 2 Yes | 3 No |
How to calculate KW what is the formula for KW.
We are using 3core 11KV HT cable for same phase for generator outgoing, the cable leakage current is high and cable heated overly what is the remidy, if we use the 3core cable for 3phases the problem is solved are not?
why the India electrical supply transmission loss is high when compare to us
why we using capacitor in single phase motor ?
I decided to provide a 11KV / 440V Xformer in my Substaion. What are the protection required for that?
What is main purpose of chock coil and starter in florescent tube ?
what is impedence of transformer? its formula
For a load of 40HP induction motor.what will be size of Armoured copper cable require to connect the motor to starter in Star-Delta?
what is maintenance?how to explain
how many testing is necessary for 27 MVA transformer?
What are the different types of LT Cables?
How many earthing pits required for diesel generator set ? Why ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)