On the secondary side of a distribution transformer, we use
1c x 630 sq mm cable. Why dont we use 4 core cables instead
of 1 core cables on the secondary. Why we use aluminium
cable glands on the outgoing instead of brass cable glands?
Answers were Sorted based on User's Feedback
Answer / pp
As the Transformer size increases the current flowing
through LT also increases. For Transformers of 630 kVA and
above, single core cables are used for LT as the insulation
is not sufficient enough to carry large amount of current
at source (T/F Secondary)for poly core cables and leads to
phase to phase faults.
Note: current for cable at Secondary termination is larger
than at any point due to creation of multiple circuits.
Poly core cables are available in sizes upto 300 sq.mmm.
for LT .
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / k.prakashchandra
Cables of above 250 sq mm come in single core only in view
of the weight, workability and replacement.Al glands are to
be used for Al cables to avoid bi-metallic contacts.
| Is This Answer Correct ? | 3 Yes | 1 No |
all 3 current transformers (C.T) are burnt in a L.T Panel - what are the possible reasons
What are unstable systems?
why capacitor do not switch ON the DG power? (I had checked, capacitor ON in DG power that time current rating was reduced.)
The height to which the liquid in a tank to be maintained for a certain constant velocity?
In 400KV Switchyard, we have used Circuit Breaker With PIR, what is the significance of PIR & why they'r used?
what is diff. between earthing grid,earthing mess, earting grid?
0 Answers Century Rayon, Emco, Tailor Solution,
why rating of transformer is in KVA but of motor is in KW
what is the power rating of CPU, CRT type moniter, LCD type moniter,scanner Approx.
short notes on npn & pnp transisitor..........
Sir if i have 2kv ups in which 17ah 8 battries load 600watts how much back up time i get and if i put 6kv ups with the same no of battries same amp can i get more back up time please give reply exactly what is the procedure to calculate back up time for different kv,s
BSNL TTA EXAM QUESTION
HOW TO CALLICULATE RESITENCE,REACTANCE AND IMPEDENCE VOLTGE OF TRANSFORMER 13.33 KVA 144/240 VOLTS 93/56 A WITH FORMULA
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)