Sir if i have 2kv ups in which 17ah 8 battries load 600watts
how much back up time i get and if i put 6kv ups with the
same no of battries same amp can i get more back up time
please give reply exactly what is the procedure to calculate
back up time for different kv,s
Answers were Sorted based on User's Feedback
Answer / dheeraj
AH stnads for Amp hour capacity, Back up depends on the AH
capacity of the Battery.
For Examlpe if you have 100 AH batery of 2 volt, it means
at 2 volt and 1 amp load can give you 100 Hrs backup OR at
2 volt for 2 amps load the back up time will be reduced to
half i.e. for 50 Hrs only. simply You calculate A x H.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / k.prakashchandra
The KVA of UPS has nothing to do with back up time . The
back up time is = stored energy in watt hour/load in watt.In
this case Back up time = 17 x 8 x 12 (voltage of each
battery)/ 600 =2.72 hour
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / krish
back up depending on you'r load so you have 17ah battery.
so u can put on the full load 600w taken 2.6A so this
is given backup for 6oow 6.5hr
| Is This Answer Correct ? | 1 Yes | 0 No |
WHAT IS THE PARTIAL DISCHARGE TEST?
Three way plug point is there ,in that plug why we need earth pin is bigger than compare with phase and nutral pins?
3 ph motor connected in star delta starter. when we start the motor it run in star but when in is going in delta it trips the main incoming supply. why?
What will the effect on a motor designed at 60 HZ, and operated on 50 HZ ??
CONSIDER A 415V/200V STEP DOWN TRANSFORMER.CAN WE USE USE IT AS STEP UP TRANSFORMER BY GIVING 200V IN SECONDARY AND TAKING OUTPUT FROM PRIMARY?
How many no. of earthing pits required for commisioning a new 320KVC DG Set????How????
If the kvar rating of capacitor bank is 600 kvar at 525V then what it's rating at 415v.
In a Synchronous generator, Can AC voltage be used instead of DC voltage in field winding of rotor to produce AC power?
when power transformer is flashed which gas is produce in side?
Why power factor does not occur in DG set ?
What is C-factor?why it is required to consider in fault short circuit calculations?
What is the effect on Power factor and capacitor when your company load is more than 70 % of welding transformer
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)