Sir if i have 2kv ups in which 17ah 8 battries load 600watts
how much back up time i get and if i put 6kv ups with the
same no of battries same amp can i get more back up time
please give reply exactly what is the procedure to calculate
back up time for different kv,s
Answers were Sorted based on User's Feedback
Answer / dheeraj
AH stnads for Amp hour capacity, Back up depends on the AH
capacity of the Battery.
For Examlpe if you have 100 AH batery of 2 volt, it means
at 2 volt and 1 amp load can give you 100 Hrs backup OR at
2 volt for 2 amps load the back up time will be reduced to
half i.e. for 50 Hrs only. simply You calculate A x H.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / k.prakashchandra
The KVA of UPS has nothing to do with back up time . The
back up time is = stored energy in watt hour/load in watt.In
this case Back up time = 17 x 8 x 12 (voltage of each
battery)/ 600 =2.72 hour
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / krish
back up depending on you'r load so you have 17ah battery.
so u can put on the full load 600w taken 2.6A so this
is given backup for 6oow 6.5hr
Is This Answer Correct ? | 1 Yes | 0 No |
how a vibration switch's high signal will going to trip the motor? can u explain with some examplesand wiring diagrams?
what is the rating of power generation in india?
What are the effects of adding a zero to a system?
What is the purpose of Vector Group in transformer?
1 Answers Andritz, ThyssenKrupp,
what is the differences between microprocessor and general purpose computer
what are the sections in a high voltage system(eg:incomer,buscoupler,isolator
Difference between hopkinson and swinburne's test
which is the best, A/C DRIVES or D/C DRIVES for cranes,...... ...and why......?
What is the function of pulse transformer?
What is the previous name of Cox's Bazar
what will happen if the frequency supplied is more than the frequency of the instrument...?
IN MY INDUSTRIES 125 HP MOTOR USED FOR THAT ONLOAD AMPS UP TO 280 SO CAN I USE ONE LOWER KVA DG SET WITH STEP UP TRANSFORMERS THAT MEANS WITH LOW POWER INPUT TO GET CONSTANT HIGH POWER OUTPUT EG:125KVA DG SET = 250 KVA STEP UP TRANSFORMERS