all 3 current transformers (C.T) are burnt in a L.T Panel -
what are the possible reasons
Answers were Sorted based on User's Feedback
Answer / animesh daripa
Suddenly disconnected the load from L.T side. The secondary of a current transformer is not disconnected from its load while current is flowing in the primary, as the transformer secondary willattempt to continue driving current across the effectively infinite impedance up to its core saturation voltage. This may produce a high voltage across the open secondary
Is This Answer Correct ? | 8 Yes | 4 No |
If measuring cts,may be due to defective rotary phase
selection switch- CTs open circuited
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / onlykk
The CT connection point of Energy meter/MDC which was connected in the system is opened.
Main cause CT points opened at any where.
Is This Answer Correct ? | 0 Yes | 0 No |
why the starting current of a motor is high?
How do you protect your appliances from harm in case of neutral failure in a three phase power supply set up.
i am getting to neutral earth voltage zero ,is this a perfect earthing ?
why and where we use early make & late break contacts in protection?
For a spring controlled governer the relation F = ar+b (F is the controlling force, r is the radius of rotation a and b are constants), indicates that the governer is
Why transformer neutral earthing? What is advantages?
why contactors are used ...? is contactors and relays are same ...?
What is the power requirement of tamil nadu for one month?
Why are the HV motors are connected in star connection?
Why in KVA diesel engine? Why not KW
Is Indian railway uses 25000v ac or dc?
how can we detect that which is receiving side and which is sendind end of a trnasmmison line by just seiing it?i.e its which end is coming from genertaing and distribution side?