why rating of transformer is in KVA but of motor is in KW
Answers were Sorted based on User's Feedback
Answer / krish
1)Transformer is an static device and original it has no PF(
when no load is connected to it),only real power is taken
into account,motors use both real and reactive power for
working so its rating is in KW
2)in transformer iron loss and copper loss is taken in
consideration so KVA is used
Is This Answer Correct ? | 15 Yes | 0 No |
Answer / asmita
in a T/F Copper losses depends on Current & iron losses
depends on Voltage.T/F being a static device windage
& friction losses r nt present there.Therefore T/F rating
is always in KVA.
Is This Answer Correct ? | 1 Yes | 3 No |
Answer / vinit tomar
both ratings are same
because
transformer can works on high voltage & current so we use the rating KVA =killo volt ampere
P=VI
here A is used to denote current in amperes
AND motors can works only low voltage
so we used rating for motors WATTS
P=VI watts
P=I.IR
Is This Answer Correct ? | 2 Yes | 4 No |
Answer / krish
A = Appearing as a first letter denotes Aluminium Conductor.
Y = TROPODUR (PVC) Insulation or TROPODUR (PVC) Sheath
depending on the position in which it appears.
2X = TROPOTHEN-X (Cross-linked Polyethylene) Insulation.
W = Round Steel Wire Armouring.
WW = Double Round Steel Wire Armouring.
F = Formed Steel Wire (Strip) Armouring.
FF = Double Formed Steel Wire (Strip) Armouring.
C = Metallic Screening (Usually of Copper).
CE = Metallic Screening (usually of Copper) over each
individual core.
Gb = Holding Helix Tape (of Steel)
Wa = Aluminum Round Wire & Aluminum Formed Wire (Strip) Fa
Armoring
Is This Answer Correct ? | 1 Yes | 14 No |
how ship earthed?
Why does amplifier gain reduce?
What are the tests carried out on transformer while testing at sites?..Pls explain me in detail
For a load of 40HP induction motor.what will be size of Armoured copper cable require to connect the motor to starter in Star-Delta?
explain wiring system
how to find out speed of single phase motor
why we use 20 KV, 10KA LA on 22 KV Line
A powerplant has 8 gensets operating in grid parallel mode. In one genset sometimes there is pf variation and kvar variation. The plant operates in pf mode. When this variation is observed the load is stable, voltage is also stable, freq and genset speed is also stable. How will you check the functioning of pf card. What shall be the ideal output vdc of the pfc, from there it is input to AVR?
I am having a DG set.The 415 V from Generator is step up to 460 v and then the same is used for Induction furnace. before Step up, I am connecting LT load to my factory use. When Induction furnace is in service from DG, when i try to start a motor, the generator is tripped.Please tell me the reason.
Why we use Electrical energy rather than any other type of energy, mostly? Explain behavior of open secondary CT and short circuited secondary PT in energized condition?
how to set the transformer differential relay
how many testing use in power transformer?tell equipment names?