why we use star and delta connection?why we donot give the
supply directly?
Answers were Sorted based on User's Feedback
Answer / murali
At the time of starting motor current will be high .Need to
reduce the starting current for protection of winding in
motor. Since star connection reduce the current ratting at
starting condition so we use the star connection after
normal speed the motor will run in delta connection as
normal current
| Is This Answer Correct ? | 150 Yes | 14 No |
Answer / abhishek goyal
We use star delta for mostly above the 10hp motors (we use
dol starter). When we connect dol starter to above 10hp
motor it will be trip because it take high current during
starting time approx 6-7 times of rated current. If we using
star delta starter it will work because in star Iph=IL and
Vl=Vph/1.732 so that in starting time it take less voltage
then delta and it torque also less and speed also less as
per electrical or practical application at that time torque
is 1/route3rd or 1/1.732 time so that current also less by
1/route3rd or 1/1.732 times. After getting speed it will
connecting into the delta position.
If directly connected with supply it will burn out or damage
of some other electrical equipment because of high
current.insulation of motor also damage or burn.
| Is This Answer Correct ? | 34 Yes | 5 No |
Answer / gopala rao yalagala
Star delta conection 3ph sq induction motors above 10 hp motors at the starting time of taken the motor high torque so star conection produce high current minium 10 seconds motor running the star conection ofter taken the normal current because delta conection
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / ashresh
when start the motor high currents getting it can be damage of motor but that we use star delta connection to the motor
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / abinash
3 phase squirrel cage induction motor above 10hp with load and DELTA connected will takes high starting current due to starting torque.When motor start with star connected it takes low current but not reach to its rated efficiency.For this purpose motor above 10 hp started with star and after few second when starting torque reduced it will shifted to DELTA to achieve higher efficiency with control FLC and without loss.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / suresh ram
10 hp or Above motor take starting current 6-7 times to normal current. To reduce current used star few times the after moto will be run delta the give be full efficiency.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / rupam dwivedi
reduse the starting current@starting torque
| Is This Answer Correct ? | 1 Yes | 0 No |
first answer is two or three fluxs(torqres) are required for the to rotate the motor and to produce emf in the generator that why we r using three winding connected like star and delta.but single phase motors also used in small applications .and second answer is to reduce the stating speed of the motor .
| Is This Answer Correct ? | 4 Yes | 6 No |
Answer / ravi chaurasia
Dear Murlali, i would have been totaly agreed with u if the
qestion would have been : why we use star delta starter ?
We all know any induction motor works on the principle of
mutual induction ie when a 3 phase supply applied to stator
winding, 3 phase flux is set up in the air gap which links
with the rotor winding and it induces an emf in the rotor
winding and causes a current to flow in the rotor winding
and in responce to that rotor tries to oppose the every
cause which produces rotor current ie three phase rotating
flux and in responce to that it starts rotating.
Now if motor is not connected either in star or delta it
will not be able to produce 3 phase rotating flux in the
air gap and hence they are either connected in star or
delta.
| Is This Answer Correct ? | 10 Yes | 15 No |
Answer / rakesh
star delta connections r used to reduce the numb of
conducors required for pow transmission. Generally we gen
3ph pow, so there vl b 3 coils in generator 2 gen 3ph pow &
each coil vl have 2 point ie. start & end terminals of
coil. so totally 3*2=6 conductors r req to transmit pow
which increases the transmission cost, so in order to
avoid this v use star delta
| Is This Answer Correct ? | 3 Yes | 12 No |
What is nyquist contour?
what is the difference between switchgear and circuit breakers and is there any difference between outdoor and indoor switchgear and circuit breakers , and how would you differentiate between switch yard and substation and grid station . thanks
what is mathed of check the D.C MOTOR 181 KW (ARMATURE AND FIELD) WHAT IS THE MATHED OF CHECK THE THYRISTOR MODULE (HIGH CURRENT)
in electrical control panel. how can i choose the cable rating. (example - 11kw motor, 18-25A mpcb}
Why synchorised generators are used for the production of electricity?
Whether it is possible to measure energy at the input of rectifier transformer (12 pulse with very high odd harmonics)
CAN WE CALCULATE THE NEGATIVE SEQUENCE AND ZERO SEQUENCE REACTANCE OF A GENERATOR USING ONLY ITS RATED VOLTAGE, KW, PF AND SYNCHRONOUS REACTANCE??? IF YES, THEN HOW??
What are test signals and their significance?
how to calculate the ct burden?
what are corona losses
How to calculate fault level of 11 KV system
What is the effect on in Zone and out zone fault if Phase side CT is Vk/2<30 mA and Neutral side is CT is Vk/4<30 mA for Transformer REF protection
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)