Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to calculate the size of cable for 100 kva load,?can
somebody tell me with a formula

Answers were Sorted based on User's Feedback



how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / naresh kumar dhal

100kva load has total current of-139 amps.

if we consider derating factor=0.8

Then total current=139/.8=173 amps

For 173 amps we can use 120 sqmm cable.
Its current capacity=1.5*120=180amps

Is This Answer Correct ?    34 Yes 17 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / piyush

what is mean of x ?& how to clculat cable sizes 35 -------
sqmm please tel in detail

Is This Answer Correct ?    18 Yes 10 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / sridhar nayak

P=1.732VI
u calculate i,take voltage 415V for three phase LT
if i=x,than cable size x=20 or 30
cable sizes are-35,75,95,120,150,185,240,300,400sqmm
it apllicable for alluminium cable only

Is This Answer Correct ?    16 Yes 15 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / kather oli

100 kva 140amps.so, 4core armoude aluminium 100 sqm 4 core
correct cable

Is This Answer Correct ?    13 Yes 13 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / manoj patel

From KVA , You get value of Amp.
By using standard cable catloge (size versis capacity)
you can find cable size.
That is only way to find cable size.From my point of
view there is no standard formula for that.

Is This Answer Correct ?    8 Yes 11 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / venkatesh

1kva=1.7amps
100kva=170amps
firstfall we are find out cable item aluminium or copper
aluminium gives 1sqmm=1amp sand copper gives 1sqmm=2amps
but we can use more than 2amps beacuse cable long time will
not come.we have to select aluminium cable for 185sqmm
beacuse total load is 170amps 185sqmm is enoff

Is This Answer Correct ?    14 Yes 22 No

how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula..

Answer / haiat

1KVA=1000VA
1000VA=1000/230A=4.34A

Is This Answer Correct ?    9 Yes 19 No

Post New Answer

More Electrical Engineering Interview Questions

how to calculate voltage drop in long distance cable? for an e.g lamp of 12 volt ac ,300watt is 90 meter away from supply i.e (x'mer 230 v / 12v)and i m getting 8 volts at lamp terminal ....

1 Answers  


1.what is the difference between transformer differential and busbar differential.2)why we are using 2 slope for trafo diif and 1 slope for busbar diff.3)what is the purpose of metrosil and stabilizing resistor in high impedance relay circuit.4)how metrosil reduce the peak volage.5)what is the funtion of stabilizing resistor

0 Answers  


How we can calc. the Backup time of a battery Bank???

6 Answers   Emerson,


how to choose the cable rating for load (KW)? EXAMPLE.50KW load

14 Answers   ACC, NCUI, Polycab, PowerSol, Siemens, SW,


what is the contact resistance of sf6 circuit breaker??

2 Answers  


What is meant by Low Resistance Cable and High Resistance Cable.

0 Answers  


how to wiring 20 hp motor get completated?

1 Answers   Alchemist,


How many type of ht insulator with name

1 Answers   Bhushan Power Steel,


how was your last weekend.

0 Answers   HCL,


what is the ohmic value of transformers

1 Answers  


How do we calculate tranmission line losses of a 132 KV tranmsission line. Please give some quick tips?

2 Answers  


What should be the conservator minimum oil level required in 2 mva transformer

2 Answers   JSW,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)