what will be the
energy loss =?
Voltage drop = ?
Conductor resistance at 20 degree C = ?
Temprature convertion Factor at 50 degree c = ?
on ACSR DOG Condutor at following data.
distance = 4.8 kM
Load = 2980 kWh
Size of Conductor = 6/ 0.186
Volt = 11 kV.
Answer / k.prakashchandra
You have given the load in Kwh.Dog conductor resistance at
20' C is 0.281 ohm/km
Is This Answer Correct ? | 3 Yes | 2 No |