Answer / krishna r
if there any short occur, the heavy current will pass
through in that top point. its size is large because it
should be low resistance, according to resistivity = RA/L,
ie, Area is inversely proportional to resistance. so if area
increases , resistance decreases.......... please reply if
you find answer wrong .....
| Is This Answer Correct ? | 61 Yes | 12 No |
Answer / k.prakashchandra
The topmost hole is for earthing and it is connected to the
body of the equipment.In case of severest earth fault ,the
fault current may go upto 25 A ( depending on earth
resistances of both Tr neutral and earth wire) and hence the
size of the pin is larger.Further the top can be fixed in
one position only so that neutral and phase wires are not
interchanged.And also ,with the third larger pin the top
stays firm in position.The pins are slitted so that they
remain inside the holes tightly pressed.
| Is This Answer Correct ? | 25 Yes | 1 No |
Answer / shahid
If there is any fault like ground. and we connect the plug
into socket , first will connect top point. and fault
current flow through top point.Not follow any other route.
Also we will save from sock.
This is only for safe use.
| Is This Answer Correct ? | 8 Yes | 4 No |
Answer / aayush shrivastava
if we apply the power in any conductor,their is some charges
will comes on the surface of the conductor, for discharging
that charge we use the hole that will connected through the
earth,the resistance of the wire low so the size is large .
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / tharanidharan a
In a three pin plug ,the base two pins arranged serially are
PHASE and NEUTRAL. and the top most large sized pin is made
for grounding purpose which is used to protect the device from
shorts(high and low voltages)
example:
when a three point charger is inserted the top larger pin will
touch first than the rest so that the device is prevented by
ground
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ramkumar
we know that current always choose low resistance path. as
per the resistance formula when the cross section is large
ultimately the resistance is less. another reason is the
remaining pins are designed for carrying rated currents. say
6 A. the earth terminal designed to carry more than the
rated current during fault condition.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pkb
Top point is for earthing. The hole size is large (1) to
flow fault current which is very large (2) secondly to
distinguish between phase and neutral point.
| Is This Answer Correct ? | 0 Yes | 2 No |
What are the major types of Curent Transformers?
What is the size of cable to be used for a Space Heater in UPS 160KVA of carrying 10 Amps current with 240 V ,1 Phase?
How to calculate KW saving for power factor correction from 0.92 to 0.98 at 350KW load?
What is the use of 1:1 isolation t/f in any circuit...?
An AC Motor to give DC supply what happen the motor.whats the problem are create.
What is LCI drive & how does it work & why it is used?
What happens with squirrel induction machines if the ends of rotor conductors are kept open? Explain
why the under of transformer platform is filled with rock stones.
10 Answers TNEB Tamil Nadu Electricity Board,
What is advantages of ungrounded neutral?
why the transmission side of the generating transformer is always star??
How I calculate the ELCB for circuit breakers?
Why do series motors have high starting torque?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)