why are caluculte transformers or dg's in kva does not
caluculate in kw
Answers were Sorted based on User's Feedback
Answer / bharani
KW is for unity power factor. But it is not so when you have
inductive load where PF may vary any were between .5 to .99.
Hence ratings are given in KVA.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / aftab alam
because transformer or DG are energy convertor not consumer
and KW is active power being consumed , transformer and DG
do not consume any power except some losses, hence these
are rated as KVA free from power factor
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / santhosh
transformers and dg's are inductive loads they are carying
capacitance and inductance so capacitive reactance and
inductive reactanctance .ie called in kva
Is This Answer Correct ? | 0 Yes | 0 No |
why ss stablity limit is more transient stablity limit?
what you mean by current? what you mean by voltage? what is difference between star and delta connection in motor side?
dear friends, we are use 130 hp load run with 0.98 power factor ( 38KVAR capacitor connected ). if we need improve the the power factor to 1 (unity). how much kvar capacitor to be add. have any formula? please share with me.
What is the meaning of high reputuring in HRC fuse.?
onan full form
We have one 500KVA transformer. We have tested REF relay and commissioned. After one and half year, due to some ground fault in one of the DB circuit Transformer tripped by REF relay. What will be cause and remedy. Please advise?
what is the difference in MCB, MCCB, RCCB, ELCB, & MPCB (motor protection circuit bracker)
12 Answers Afcons, Bhel, CIHSR, DCS, IOCL, L&T, Lupin, Siemens,
how much earth resistance consider to commissioning the transformer?
Please help me.What are the difference between two wire, 3wire, and 4 wire in electric meter?
What is AVR? Explain the function AVR?
sir i am ece engineer.i want to job in power plant.what is the best option for me as electrical engineer or instrumentation engineer?pls reply me.
why the field winding in dc motor is not short circuited eventhough dc supply is applied across the winding