why are caluculte transformers or dg's in kva does not
caluculate in kw
Answers were Sorted based on User's Feedback
Answer / bharani
KW is for unity power factor. But it is not so when you have
inductive load where PF may vary any were between .5 to .99.
Hence ratings are given in KVA.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / aftab alam
because transformer or DG are energy convertor not consumer
and KW is active power being consumed , transformer and DG
do not consume any power except some losses, hence these
are rated as KVA free from power factor
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / santhosh
transformers and dg's are inductive loads they are carying
capacitance and inductance so capacitive reactance and
inductive reactanctance .ie called in kva
| Is This Answer Correct ? | 0 Yes | 0 No |
what is droop control?
Thumb rule of cable size(rm>30 rm)X multiplying factor=ampere
0 Answers Kazi Farms, SKI Carbon Black,
at which voltage level arcing ground is occurs ??????????
different types of electrical cable?
what are effects of harmonics in the three phase a.c power system ?
what is rms value?
how to reduce humming noise in transformer?
l&t switch FN 63 handle position can we change
A double circuit with dog conductor 66KV Transmission line from wind farm evacuation to feeding substation having capacity of 25MW for transmission. Can same transmission network be considered for further expansion of Power & how much in MW. If we need to expand next 10-15 MW more will there any augmentation is required in transmission network? Kindly reply asap.
Can the Neutral and Body Earthpits of a transformer conncted together by Earth strips under ground.
what is the meaning of vcc
I have carried out wiring for lighting in a shed in Industrial area which contains Metal halide lamps & have balanced in 3ph.Now when we put all the lines on in the daytime the current taken at 3phases at MCB comes to be equal i.e.28,29,28Amps respectively but in the night time i.e between 7p.m.to 11p.m. at the same MCb the current is 52,59,62Amp, though I have fit 63A MCB it is tripping in the above period.What may be the reason.? Note: This industry is located in industrial area where majority of steel ingot manufacturing plants are there. Whether this may be due to harmonic? what should I do to overcome above problem.pl suggest urgently.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)