I have carried out wiring for lighting in a shed in
Industrial area which contains Metal halide lamps & have
balanced in 3ph.Now when we put all the lines on in the
daytime the current taken at 3phases at MCB comes to be
equal i.e.28,29,28Amps respectively but in the night time
i.e between 7p.m.to 11p.m. at the same MCb the current is
52,59,62Amp, though I have fit 63A MCB it is tripping in
the above period.What may be the reason.?
Note: This industry is located in industrial area where
majority of steel ingot manufacturing plants are there.
Whether this may be due to harmonic? what should I do to
overcome above problem.pl suggest urgently.
Answers were Sorted based on User's Feedback
Answer / ankurjha
May be some other load is coming in line at night time. see
for unautherized taps in line..
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / karthik
better change all mh fitting to other energy efficient
fittings atleast change the copper wound ballast to
electronio ballast
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / h r jadhav
pl check the maloperation of mcb or correct rating of mcb/
secondly the power factor may be very low of the metal hal
lamps during day time that may be compenseted by bus
capacitors and which are disconnected at the time of no
work. there by increasing current and mcb get tripped/ pl
use energy efficient electronics ballast.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
You should allow 5% to 10% tolerance for MCB and
meters.There could be temporary additional load also.
Is This Answer Correct ? | 0 Yes | 0 No |
What is the problem if we connect a weak capacitor to the system? is that profitable or Loss?
What is the knee point of voltage of CT?
What is mean by diversity Fator?
the circuit having same properties in either direction is known as.......
1)What will you do if main incomer VCB fail in your site ?
Hi.. I am a BE GRaduate in E&E. I have 8.5 Experience in Tendering & Estimation field. I have done SAP SD course few years back. But due to some reason i failed to get job in that field and continued my own field. Now I am thinking of changing into SAP seriously. How should i go ahead???
Slow acting fuses are most often used for which application a) Lighting circuit b) heating circuit c) Motor D) Radar circuit
Why starters are using the machines???
how the characterstics of control valve being done
Why NGR is provided in sub station?
for 750 kw LT load what will be the ht kva
I am selected in OCL(Orissa cement Limited), but they have a Tech PI round their at their plant.Anybody has any idea that what kind of questions they are going to ask??Please guies help me. I am in serious headache.I have heard that huge elimination is done at there.