I have carried out wiring for lighting in a shed in
Industrial area which contains Metal halide lamps & have
balanced in 3ph.Now when we put all the lines on in the
daytime the current taken at 3phases at MCB comes to be
equal i.e.28,29,28Amps respectively but in the night time
i.e between 7p.m.to 11p.m. at the same MCb the current is
52,59,62Amp, though I have fit 63A MCB it is tripping in
the above period.What may be the reason.?
Note: This industry is located in industrial area where
majority of steel ingot manufacturing plants are there.
Whether this may be due to harmonic? what should I do to
overcome above problem.pl suggest urgently.
Answers were Sorted based on User's Feedback
Answer / ankurjha
May be some other load is coming in line at night time. see
for unautherized taps in line..
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / karthik
better change all mh fitting to other energy efficient
fittings atleast change the copper wound ballast to
electronio ballast
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / h r jadhav
pl check the maloperation of mcb or correct rating of mcb/
secondly the power factor may be very low of the metal hal
lamps during day time that may be compenseted by bus
capacitors and which are disconnected at the time of no
work. there by increasing current and mcb get tripped/ pl
use energy efficient electronics ballast.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
You should allow 5% to 10% tolerance for MCB and
meters.There could be temporary additional load also.
| Is This Answer Correct ? | 0 Yes | 0 No |
What is thef ormula to calculate the rating of a capacitor for a single phase motor
I am having a 42KW 3 phase electrical heating furnace, heating element is 80/20 nichrome material, my connections is made in such a way that 2 star connection compromising 2 coils per phase so totally 12 coils, shall if i use it unbalanced star condition (instead of 2 group of 3 phase or 1 group of 3 phase, connecting 4 phases of 5 phases) what will be the consequences and is it acceptable?
what is difference between power & distrubution transformer ?
What is the starting current of a motor?
how to reduce power loss when the tranmission under long distance?
Form fator is the ratio of?
How to run 1ph motor(230 VOLTS its full load amps is 4.5 ampa))with 480 volts main(we didn hav neutral)Thn we go for step down transformer.Our load 10 amps,so we conisder this amps in primary are secondary side
What will happen if the d.c. Shunt motor opened accidentally running on no-load has its shunt field winding?
why the neutral of power transformer is always earthed?
What is domestic transformer? Draw the connection of domestic transformer.
how the percentage impedance affect the transformer loading when connected in parallel.?
physical identification of HT & LT panel
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)