I've heard that most of the substations are rated in
multiples of 1.11 because of form factor.What is form factor?
Answers were Sorted based on User's Feedback
Answer / vikash
Form Factor= R.M.S value / Average value of current
= 1.11
R.M.S value stands for root mean square. It is defined as DC component of ac current which produces heating effect.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / prakash
why it is multiple of 11 means 10% considered as line loss
that why all voltage are in multiple of 11 11kv/33kv/66kv
Is This Answer Correct ? | 2 Yes | 1 No |