HAI,I HAVE 6,60KW MOTOR FEEDERS IN MY MCC PANEL.HOW CAN I
DO MY SETTINGS FOR
OVERLOAD,SHORTCIRCUIT,GROUNGFAULT,INSTANTANEOUS TRIP
FUNCTION IN MY 4000A CIRCUIT BREAKER?
Answer / k.prakashchandra
Set OCR at 110 % of rated current, ground fault at 10-20 %
of OCR,inst trip at 2 to 6 times the OCR and SC(inst) at 8
times the OCR.
| Is This Answer Correct ? | 1 Yes | 0 No |
Is there any reason that we get shock on touching phase wire because the earth is at neutral potential? Is there any reason that the earth is at neutral potential because the neutral is earthed in apower station
what is the meaning of rms value
24 Answers Fitter, IOCL, OCL,
A Question Like A Wire Is Wound Whose Resistance Is Some 132. 44647 Ohms. If A Voltage Of 30 mv, 296 Ma Current Is Applied To It What Is The Resistance.
What is the minimum distance between MV busbare (P to P & P to E) as per some standards
How can I calculate ISF of current transformer?
0 Answers Cigniti Technologies,
What type of a DC motor would you use for a lift?
HOW TO CALCULATE THE ILLUMINATION IN INDOOR LIGHTING?
what is a speed of rotor when we give supply to stator of 50hz and as well as rotor of 60hz of an induction motor?????
how a circuit breakers work at fault condition .plz give a specified answer.
do we convert single phase line to three phase at minimum cost?
WHY POLARITY TEST OF CT IS VERY IMPORTANT IN SWITCHGEAR
Which type of starter to used which type o motor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)