HAI,I HAVE 6,60KW MOTOR FEEDERS IN MY MCC PANEL.HOW CAN I
DO MY SETTINGS FOR
OVERLOAD,SHORTCIRCUIT,GROUNGFAULT,INSTANTANEOUS TRIP
FUNCTION IN MY 4000A CIRCUIT BREAKER?
Answer / k.prakashchandra
Set OCR at 110 % of rated current, ground fault at 10-20 %
of OCR,inst trip at 2 to 6 times the OCR and SC(inst) at 8
times the OCR.
Is This Answer Correct ? | 1 Yes | 0 No |