how the actually positioner of control valve working?
where we gave 3-15psi pressure to I/P converter where it is firstly applied ?- on I/P to positioner then what happen?
is control valve operate on 3-15 psi or its bench pressure?
Answers were Sorted based on User's Feedback
Answer / himanshu amin
valve positioner is having three air connection. 1. Air
supply,2. i/p 3 to 15 psi from i/p converter. 3. o/p to
control valve. suppose you are giving 9 psi to valve
positioner. valve positioner will supply o/p for 50 % valve
opening. the feedback arm of valve posioner will give
feedback to valve positioner according to valve position.
| Is This Answer Correct ? | 9 Yes | 1 No |
Valve Positioner actually working is following steps:
Supose valve is air to open and right now is at it's normal condition.at this condition positioner will not send any air to control valve.
Now given command to 10 percent to open
So first positioner will send air strat to applying air to actuator ,when actuator will get sufficient air to perform operation it will start opening.
Now when the valve will reach to the set point mean 10 percent,positioner will stop the air and maintain valve opening at a set point.
This thing is same in the closing
Thous positioner is works to control the opening and closing .
| Is This Answer Correct ? | 1 Yes | 0 No |
what is difference between DO and DI
What are Sinking and Sourcing IO Cards
what is the well head protection system?
What is the basic principle of vibration measurement by BENTLY NEVADA vibration measurement system? and Why it gives the -ve voltage output?
14 Answers Ensol, GNFC, Reliance, Siemens,
What is Cavitation in a control valve?
Explain , how timer based pneumatic control valve will work ?
Why three wire is using with a RTD?
if we open the inlet of an air regulator ,how it will affect the out put of regulator? (out put of regulator is using to operate an on-off valve.it is an air to open valve,and valve is in open position.my doubt is air regulator will hold the valve in open or not,if there is no consumption or leak in regulator out put side ,we only loose the input pressure.)
How to check the SCAN time of DCS ,n dont give therotical answers .How to check the SCAN time of DCS during FAT?
model question paper of instrumentation for Jindal GET 2010.plz reply sudhanshukumar08@yahoo.com
what is meant by turn down ratio?
What is passive connection of instrument in different types of IO module?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)