Answer / pavan wagh
At high pressure in pressurized vessel ultrasonic signal gets suppressed substantially ,same is the case with strong vacuum where medium (air) of signal transfer is absent.
In both cases DP transmitter is the best choice for good accuracy. For level measurement with DP transmitter density compensation is essential,as liquid (water) density changes at high pressure and high temperature.
Is This Answer Correct ? | 2 Yes | 0 No |
What is 1:1 redundancy ?
1. Pl. send details about different types Gas Analyser, like Co2, O2, SOX/NOX, etc. with calibration procedure. 2. How to calibrate H2S gas detector in field?
How will u convert the mmh2o in mass or Volumetic flow rate in DP Flow Transmitter. Give me the Brief explain using the formula
1 Answers Walchandnagar Industries,
What is the difference between instrument earthing and normal earthing? and why is it necessary to do so?
What is the purpose of the analyzer in petrochemical plant?
0 Answers ENI, Lakshmi Machine Works,
Difference between ultrasonic flow meter and radar type flow meter
2 Answers Dodsal, Qatar Petroleums,
Why the Air Tank Accumulators required for the single acting actuators SDV's or BDV's as I see in some Schematic diagrams of ROTORK ??
Why we are using PLC instand of DCS in ESD System? can u explain any one?
what is isolation Transformer???...
difference between null and deflecting instrument.
Why does a pressure gauge installed on reactor, doesn't have any vent line below to release the pressure? Is it any kind of designing mistake or it actually does not require any vent line? And if it does not require any vent line below it then how we are gonna release the pressure built inside the pressure gauge?
0 Answers Process Control Technologies,
what is difference b/w tube and pipe ?
6 Answers BSL, Descon, Kirloskar,