Does Lightening arrest requires Earthing?..
Answers were Sorted based on User's Feedback
Answer / gayathrikandaswamy
yes,lightning arresters require earthing.
| Is This Answer Correct ? | 15 Yes | 0 No |
Answer / maheshkumar
yes, it requires earthing.. otherwise it cant divert the
bulk power....
| Is This Answer Correct ? | 13 Yes | 0 No |
Answer / jairaj shetty
yes the role of a lightning arrest is to trap the hi
voltage electric arc produced by lightning and sink it to
the ground , so it is installed in the highest point of a
building and a conductor is coupled from the arrester to
the ground .
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / karthi
Yes, its mandatory, otherwise it can spoil the equipments.
the earth pit value is <1ohm
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / raziq ulla
Yes required,
Lighting arrester means it will arrest the surge voltage
caused by lighting, and it must be installed at the top of
the building to safe gaurd the building from heavy (surge)
voltage, if the Lighting arrester is not earthed properly
high voltage will damage the building so that proper
earthing is neccessory to safe grounding of surge voltage.
| Is This Answer Correct ? | 1 Yes | 0 No |
what is the function of buchhos rely in transformer
wht is the purpose of the earth electrode other then earthing
What accessories required to give the motor with given circuits and do you know the ratings of those accessories?
What are the effects to a distribution transformer rated 10Kv with ratio 10Kv/0.433Kv, 3phase 50hz for example but fed with power supply of 11Kv?
what is the difference between relay and a contactor.
What is effect on in zone and out zone fault if CT chosen for phase side is Vk/2<5mA and Neutral side is Vk/2<15mA on REF protection of Transformer
We have 2 Nos. Transformer with the capacity of 2000KVA and 1250 KVA and currently using only one 2000KVA T/R during operational hours while non- operational hous 1250 KVA T/R also used to reduce T & D losses. Similarly, 2 capacitor bank of 500KVAR and 300 KVAR also installed to balance reactive power. Now problem is around 1000 KW load PF is not maintaning 0.99 as 350 KVAR capacitor is in healty condtion. Now the PF is maintain 0.95 to 0.96.
why we can't use more then 50 hz in india ? Is it possible ?
why transmition and distribution and genaration of voltage in multible of 11 means 220v,440v,11kv,22kv,,,...so on
can anibody tel me on what basis the transformer vector groups are determined????
what is the difference between squirrel cage & slip ring induction motor?
17 Answers College School Exams Tests, NTPC, Ramyaa Electro Gear,
What will be the resultant out put voltage when two different voltage rating batteries are vconnected in parallel? pls. answer with example if available.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)