We have 2 Nos. Transformer with the capacity of 2000KVA and
1250 KVA and currently using only one 2000KVA T/R during
operational hours while non- operational hous 1250 KVA T/R
also used to reduce T & D losses. Similarly, 2 capacitor
bank of 500KVAR and 300 KVAR also installed to balance
reactive power. Now problem is around 1000 KW load PF is
not maintaning 0.99 as 350 KVAR capacitor is in healty
condtion. Now the PF is maintain 0.95 to 0.96.
Answers were Sorted based on User's Feedback
Answer / arvind
You please check out the location of the capacitor banks
means whether it is away from the load or not if it is away
from tha load then power losses will be there and affects
the power factor.
secondly, if the load (1000kw) is variable means motor,
then it is difficult to get power factor 0.99.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / muhammad azeem butt
we know that transformer is a inductive device it also
effect on our pwer factor lagging.
Power and distribution transformers, which work on the
principle of electron-magnetic
induction, consume reactive power for their own needs even
when its secondary is not
connected to any load. The power factor will be very low
under such a situation.
To improve the power factor it is required to connect a
fixed capacitor or a capacitor
Sl.no kVA rating of the transformer kVAr required for
compensation
1 upto and including 315 kVA 5% of kVA rating
2 315 kVA - 1000 kVA 6% of kVA rating
3 Above 1000 kVA 8% of kVA rating
| Is This Answer Correct ? | 1 Yes | 0 No |
why transformer rating in kva
What is Co-generation in the context of electrical power systems?
I WANT TO know WHICH WAY IS BETTER FOR CONNECTION BETWEEN POWER TRANSFORMER AND MAIN DISTRIBUTION PANEL. 1-IS BETTER WE USE CABLE? 2-IS BETTER WE USE BUS DUCT? my transformer rate power is 2500KVA
How to calculate load requirement of a 50 flat apartment with 5 kw each unit,sizing of cable,transformer
How to calculate the diesel generator efficiency? what details are required to identify the running diesel generator sets with 1000 kVA & 180 kVA?
11 Answers Greeves, Sudhir Power,
what is the VA(Volt-amphere)? define with calculation?
how we select fuse rating for motor?
why ac ratings are in tons?
For a 6.6kV Motor it is recommended to do megger test with 500 V d.c and not more than 5kV d.c but the Hi voltage withstand test should be performed by 12kV AC. Why the dc voltage test should be limited but AC voltage withstand test could be with such a high voltage?
why do we have spikes enough to burn electronic boards, when generators are not grounded
State Maximum Power Transfer theorem.
What is the differemce between Pulse transformer and Welding transformer.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)