We have 2 Nos. Transformer with the capacity of 2000KVA and
1250 KVA and currently using only one 2000KVA T/R during
operational hours while non- operational hous 1250 KVA T/R
also used to reduce T & D losses. Similarly, 2 capacitor
bank of 500KVAR and 300 KVAR also installed to balance
reactive power. Now problem is around 1000 KW load PF is
not maintaning 0.99 as 350 KVAR capacitor is in healty
condtion. Now the PF is maintain 0.95 to 0.96.
Answers were Sorted based on User's Feedback
Answer / arvind
You please check out the location of the capacitor banks
means whether it is away from the load or not if it is away
from tha load then power losses will be there and affects
the power factor.
secondly, if the load (1000kw) is variable means motor,
then it is difficult to get power factor 0.99.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / muhammad azeem butt
we know that transformer is a inductive device it also
effect on our pwer factor lagging.
Power and distribution transformers, which work on the
principle of electron-magnetic
induction, consume reactive power for their own needs even
when its secondary is not
connected to any load. The power factor will be very low
under such a situation.
To improve the power factor it is required to connect a
fixed capacitor or a capacitor
Sl.no kVA rating of the transformer kVAr required for
compensation
1 upto and including 315 kVA 5% of kVA rating
2 315 kVA - 1000 kVA 6% of kVA rating
3 Above 1000 kVA 8% of kVA rating
| Is This Answer Correct ? | 1 Yes | 0 No |
what is the most permissible winding temp when we conducting a generator load test?(condition no load)
what is differnt between metering CTs an protection CTs
what are the standard IR values should be of R-E, Y-E, B-E, R-Y, Y-B, B-R of VCB in closed condition and in open condition for 500KVA & 1000KVA transformers. and what is the acceptable range when tested by 5000V megger.
We are using 3core 11KV HT cable for same phase for generator outgoing, the cable leakage current is high and cable heated overly what is the remidy, if we use the 3core cable for 3phases the problem is solved are not?
In a three phase transformer(delta/star connected)when i touch one end of the bulb in any one phase and other end to earth..will the bulb glow or not..if not why?..i'm touching the bulb in star connected side...
How can w select the cable size for different rating load & also waht r factors affecting the during selection of cable?
11 Answers AB Inc, Bosch, BRB Cable, Lucas TVS, Trisome Technical Services,
Why the CT Secondary is rated as 5A generally?
what is the formulae for selcting capacitor bank to increas pf
why transformer core is eathed?
what is max. continous current of LT side of distribtion transformers? ie for25kVA, 63kVA, 100kVA, 200kVA etc
What is meant by class of CT&PT?
why delta delta connection generally not use in transformer
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)