We have 2 Nos. Transformer with the capacity of 2000KVA and
1250 KVA and currently using only one 2000KVA T/R during
operational hours while non- operational hous 1250 KVA T/R
also used to reduce T & D losses. Similarly, 2 capacitor
bank of 500KVAR and 300 KVAR also installed to balance
reactive power. Now problem is around 1000 KW load PF is
not maintaning 0.99 as 350 KVAR capacitor is in healty
condtion. Now the PF is maintain 0.95 to 0.96.
Answers were Sorted based on User's Feedback
Answer / arvind
You please check out the location of the capacitor banks
means whether it is away from the load or not if it is away
from tha load then power losses will be there and affects
the power factor.
secondly, if the load (1000kw) is variable means motor,
then it is difficult to get power factor 0.99.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / muhammad azeem butt
we know that transformer is a inductive device it also
effect on our pwer factor lagging.
Power and distribution transformers, which work on the
principle of electron-magnetic
induction, consume reactive power for their own needs even
when its secondary is not
connected to any load. The power factor will be very low
under such a situation.
To improve the power factor it is required to connect a
fixed capacitor or a capacitor
Sl.no kVA rating of the transformer kVAr required for
compensation
1 upto and including 315 kVA 5% of kVA rating
2 315 kVA - 1000 kVA 6% of kVA rating
3 Above 1000 kVA 8% of kVA rating
Is This Answer Correct ? | 1 Yes | 0 No |
what are 3 factors when selecting a contactor for a job?
what is the function of choke and starter in a tube light??
what is the effect of earth on capacitance in 3-phase and 1- phase transmission line?
What happened when capacitor connect series in ac circuit?
HOW THE AC GENARATOR CAN GENARATE REACTIVE POWER,HOW CAN WE CONTROL IT.AND OTHER SOURSES OF REACTIVE POWER GENARATIONS ARE WHAT.
Why we are use 11KV / 22KV / 33KV / 66KV / 110KV / 230KV / 440KV this type of ratio. why cant we use other voltage ratio like 54KV / 99KV et.,
8 Answers College School Exams Tests, Hino, ITC Infotech, Reliance, UPRVUNL,
why do the alternator doesnt have open circuited windings in armature???
We have a 62.5 KVA DG with Leyland engine and kirloskar slipring alternator. We have earthed the neutral, and another earthing for the dg body. is it necessary to isolate the dg foundation with rubber pads?
Write the current equation in series RLC circuits.
0 Answers Agilent, Integreon, ZS Associates,
In aerodynamic turbines which element is NOT there a.stator b.compressor c. Fuel intake system d.fans
what is the difference between Current transformer & Capacitive voltage transformer
How does numerical relay work?