What accessories required to give the motor with given
circuits and do you know the ratings of those accessories?
Answers were Sorted based on User's Feedback
Answer / manish joshi
1. RTD's: Resistance temperature Detectors : used to
measure the winding temperature , PT-100 is used in RTD and
normally 6Nos can be used
2. BTD's: Used to measure the bearing Temperature rise.
Normally 1pc/Bearing
3. DTT's : Dial type thermometeres with contacts/without
contacts alarm trip
4. Space Heater: Used to remove moisture when motor starts
after a very long time where moisure is present in the
surroundings. ratings 240 V 1Ph.
5. SPM Nipples: for vibration monitoring
6. Seperate terminal box for space heater.
| Is This Answer Correct ? | 25 Yes | 0 No |
Answer / pramod_wank
The answer of manish joshi is correct some correction as follows
1. RTD's: Resistance temperature Detectors : used to
measure the winding temperature , PT-100(2mA) is used in RTD
and
normally 6Nos can be used(In each winding 2nos RTD)
2. BTD's: Used to measure the bearing Temperature rise.
Normally 1pc/Bearing (In each side 2RTD used Drive side end
(BE) & non drive side end(NDE))the total 4RTD required
3. DTT's : Dial type thermometeres with contacts/without
contacts alarm trip.(DTT normally used for drive side end &
non Drive side end at max 250v,5A)
4. Space Heater: Used to remove moisture when motor starts
after a very long time where moisure is present in the
surroundings. ratings 240 V 1Ph.
5. SPM Nipples: for vibration monitoring (for drive & Non
Drive Side end)
6.Seperate terminal box for space heater(1ph,240v,300w).
7.Greasing Nipple for Drive & Non drive End.
8.Vibrating Sensor at drive side.
9.Main Terminal box to coonect the supply 415V AC.
10 Neutral terminal Box if required
11.Lifting Hook to lift the motor
12.Earting Bolt as per your electrical system.
| Is This Answer Correct ? | 17 Yes | 1 No |
Answer / nagaraj .n
insulation tester,test lamp,supply wires,rated type fuse,
( T P D T SUPPLY BOARD breaker.isolator&contactor.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / jagannath_sila
to give the motor with a given ckt we requir as motor
contact module of given rating.
in this module we get ckt
breaker.isolator&contactor.normally the contactor rating is
32 amp.
| Is This Answer Correct ? | 5 Yes | 4 No |
what will happen if ac motor given dc supply?
if the field circuit of a d.c. shunt motor running without load gets opened, then the motor will
What may be happen if neutral and earth is shorted in a substation
How line capacitance & line inductance varies with increase in height tower.
Name two types of electrical analogous for mechanical system.
how to find insulation resistance of a generator(11kv) by theoritical formula??
If DC supply is given to a transformer it may a) Work b)Not Work c)Give lower voltage than the rated voltage on secondary side. d)burn the winding
On what basis the the size of Lightning arrester for buildings are selected ?
what is the primary current in 415/415 v when secondry of dry type transformer is shorted.?
what is difference betwen genrator and alternator?
Which transformer is suitable for 220/11 kV, 60 MVA, distribution , Y-Y or D-Y or Y-D, give comparison for the same.
how to protect motor in dol starter having capacity of 30 hp.40 hp?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)