Why CT's shall not be kept open?

Answers were Sorted based on User's Feedback



Why CT's shall not be kept open?..

Answer / rajeev.m.l

When ct connected,that act as a stepup transformer so there will be produce a arc between the terminals of the secondary of CT.

Is This Answer Correct ?    7 Yes 4 No

Why CT's shall not be kept open?..

Answer / abdul moin

when a CT in connected to the transformer is for the
current reading to know the amps folowing through the
conductor. we keep the terminal close because of the
secondary side voltage will be rise. thats why when we
remove the meter for the maintenance purpose we provided a
short link for close the terminals inorder to avoid high
voltage at secondary.


i Hope this answer is satisfy you......

Is This Answer Correct ?    4 Yes 2 No

Why CT's shall not be kept open?..

Answer / richard harris

There is an inaccurate theory that has been in the electrical discipline for decades, and that is - if you open circuit a Current Transformer (CT) under load it can produce millions or infinite voltage.

It is the character of a CT to develop the voltage that will drive its current through its load.
(Current transformer circuits are generally a low impedance load.)

When one opens a CT circuit, to the CT - it sees an infinite resistance, and tries to develop an infinite voltage across an infinite resistance, therefore, the voltage across an open circuit CT circuit increases until the core of the CT is saturated. Once the core of the CT is saturated - it can not produce a higher voltage, - this is true for air core or iron core CTs.

There is a limit to the voltage that can be developed across a CT.

In the case of an air core CT the voltage increases until the air of the CT is saturated.
In the case of an Iron core CT, the voltage increases until magnetic flux saturates the iron.

The limiting factor in an iron core of a CT.

When the iron core of a CT becomes flux saturated, the CT like all other transformers, can NOT produce a higher voltage. The voltage that is produced is a function of how much iron is in the core of the transformer. That is true for CTs and Power Transformers.

In some cases, a higher voltage is needed to push the current through a high impedance load. To have a CT produce a higher, the CT core will need more iron in its core.

Current Transformers are rated in classes - and the higher class - the more iron in the class of the CT, and the higher voltage it can produce. That is why CTs have to be tested to determine their Saturation Voltage against their impedance load.

Plus they have to be sized not to go into saturation during a short circuit or system fault event.

Since 1978 - I have been teaching at a college, university, and professional level. I was a NETA technician level 3 for many years, and every thing that I have taught I have had field hands on experience.

The reason that I am responding to this question, as I have never had anyone accurately explain about why not to open a CT circuit "underload." - yes you can open a CT or CT circuit ONLY if it has no load or current going through its circuit.

In teaching an Electrical Safety class on a telephone conference with 25 individuals - some when back and told the Operations Supervisor and he came and confronted me. Even Electrical Engineers and management technical have never explained it or understood it to the point that they could explain it to me.

I hope this short explanation answers your question as to why a Current Transformer, or its circuit should not be opened under load.

Should you have any additional questions, do feel free to ask.

Richard Harris

Is This Answer Correct ?    1 Yes 0 No

Why CT's shall not be kept open?..

Answer / abhishek goyal

CT always connecting into the series position. If we have
some work on the Meter, we need to short the CT terminal. If
CT in open condition (it can't connected to the meter)its
step down the current in terms of 300/5AMP (for example).
After few second or minute it will drawn the more current at
infinite level at that time CT temperature also increase. If
we can't short the CT it will make big blast or sever
damage.

Is This Answer Correct ?    0 Yes 0 No

Why CT's shall not be kept open?..

Answer / azhar ali

Basically, current transform has a few turns one or may be two at primary sides and many turns on Secondary side.If the ammeter is removed, the secondary winding becomes open-circuited and the transformer acts as a step-up transformer due to the very large increase in magnetizing flux in the secondary core. This results in a high voltage being induced in the secondary winding equal to the ratio of: Vp(Ns/Np) being developed across the secondary winding.
Turn ratio=vp (NS/Np)=> VP=480 NS=160 V &Ns=1 Then,
Tr=480*160/1 = 76800 volts
So it will be very dangerous if the secondary is opened.Therefore short the secondary of CT if the current meter is removed from the CT having primary current.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

How Many safety of Air circuit breaker

2 Answers  


which motor used in electric train ans how much volt.

4 Answers   Trimax,


we all know voltage is a force(emf), and the force always devides if 2 or more than2 loads are there but why does the voltage remains same is parallel, it must devide na ???

0 Answers   NTPC,


present we are having 0.8pf but I want increase it up to 0.99 so what is the formula for it and how can i calculate?

3 Answers   ABB,


1 amp means-how many electron flow per second. ?

2 Answers  






Dear All, If we have 8No. 11kV cables running underground that are required to supply 20MW to a new development. What is the sustained current in Amps? Please advise.

1 Answers  


what is inductive voltage transformer? what is its application and how it differs from capacitive voltage transformer?

1 Answers   NRSC National Remote Sensing Centre,


diff b/w normal grounding and resistance grounding

0 Answers  


What is the use of IGBT in UPS & its working??????????

5 Answers   Reliance,


After synchronization with grid what is the demand value QKVAR and how we will maintain that?

0 Answers  


Why consumers are charged based on Kwh basis why not on Kvah basis.

4 Answers   Unitech,


if we supply DC power to AC transformer then what its result?

15 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)