Why CT's shall not be kept open?
Answers were Sorted based on User's Feedback
Answer / rajeev.m.l
When ct connected,that act as a stepup transformer so there will be produce a arc between the terminals of the secondary of CT.
| Is This Answer Correct ? | 7 Yes | 4 No |
Answer / abdul moin
when a CT in connected to the transformer is for the
current reading to know the amps folowing through the
conductor. we keep the terminal close because of the
secondary side voltage will be rise. thats why when we
remove the meter for the maintenance purpose we provided a
short link for close the terminals inorder to avoid high
voltage at secondary.
i Hope this answer is satisfy you......
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / richard harris
There is an inaccurate theory that has been in the electrical discipline for decades, and that is - if you open circuit a Current Transformer (CT) under load it can produce millions or infinite voltage.
It is the character of a CT to develop the voltage that will drive its current through its load.
(Current transformer circuits are generally a low impedance load.)
When one opens a CT circuit, to the CT - it sees an infinite resistance, and tries to develop an infinite voltage across an infinite resistance, therefore, the voltage across an open circuit CT circuit increases until the core of the CT is saturated. Once the core of the CT is saturated - it can not produce a higher voltage, - this is true for air core or iron core CTs.
There is a limit to the voltage that can be developed across a CT.
In the case of an air core CT the voltage increases until the air of the CT is saturated.
In the case of an Iron core CT, the voltage increases until magnetic flux saturates the iron.
The limiting factor in an iron core of a CT.
When the iron core of a CT becomes flux saturated, the CT like all other transformers, can NOT produce a higher voltage. The voltage that is produced is a function of how much iron is in the core of the transformer. That is true for CTs and Power Transformers.
In some cases, a higher voltage is needed to push the current through a high impedance load. To have a CT produce a higher, the CT core will need more iron in its core.
Current Transformers are rated in classes - and the higher class - the more iron in the class of the CT, and the higher voltage it can produce. That is why CTs have to be tested to determine their Saturation Voltage against their impedance load.
Plus they have to be sized not to go into saturation during a short circuit or system fault event.
Since 1978 - I have been teaching at a college, university, and professional level. I was a NETA technician level 3 for many years, and every thing that I have taught I have had field hands on experience.
The reason that I am responding to this question, as I have never had anyone accurately explain about why not to open a CT circuit "underload." - yes you can open a CT or CT circuit ONLY if it has no load or current going through its circuit.
In teaching an Electrical Safety class on a telephone conference with 25 individuals - some when back and told the Operations Supervisor and he came and confronted me. Even Electrical Engineers and management technical have never explained it or understood it to the point that they could explain it to me.
I hope this short explanation answers your question as to why a Current Transformer, or its circuit should not be opened under load.
Should you have any additional questions, do feel free to ask.
Richard Harris
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / abhishek goyal
CT always connecting into the series position. If we have
some work on the Meter, we need to short the CT terminal. If
CT in open condition (it can't connected to the meter)its
step down the current in terms of 300/5AMP (for example).
After few second or minute it will drawn the more current at
infinite level at that time CT temperature also increase. If
we can't short the CT it will make big blast or sever
damage.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / azhar ali
Basically, current transform has a few turns one or may be two at primary sides and many turns on Secondary side.If the ammeter is removed, the secondary winding becomes open-circuited and the transformer acts as a step-up transformer due to the very large increase in magnetizing flux in the secondary core. This results in a high voltage being induced in the secondary winding equal to the ratio of: Vp(Ns/Np) being developed across the secondary winding.
Turn ratio=vp (NS/Np)=> VP=480 NS=160 V &Ns=1 Then,
Tr=480*160/1 = 76800 volts
So it will be very dangerous if the secondary is opened.Therefore short the secondary of CT if the current meter is removed from the CT having primary current.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is the meaning of TPN
What is the difference between an insulator and a dielectric?
What is the technical difference between On delay timer and a Star delta timer?
megger generates D.C. voltage while earth tester generates A.C.voltage is it true? I know for megger it is D.C generator but what about earth tester?
In a transformer, the hysteresis and eddy current losses depend upon 1.load current 2.maximum flux density in core 3.type of lamination 4.supply frequency The correct statements are (a) 1 and 3 (b) 2 and 3 (c) 1 and 4 (d) 2 and 4
we have an energy meter in a capacitor bank panel, So should we consider it's readings as energy consumption on daily basis. (when capacitor bank doesn't have any energy losses)
What is mean by discrimination of circuit breaker ?
Why r use in the tap changing x' mer.
what is the effect of vector group while phase sequence of a generator changes,whether the vector group changes or not
why use in & out Diesel line in dg set.
how to calculate overall efficiency of diesel generator set? give us a formula with an example.
What happens with squirrel induction machines if the ends of rotor conductors are kept open? Explain
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)