Is it necessary to carry out sheath test after cable
jointing? If the value is zero of such instance , is it ok
to energize the cable?
Answer / k.prakashchandra
If you get zero ohm on sheath test ,sheath continuity is
confirmed.You can energize the cable after testing insulation
Is This Answer Correct ? | 1 Yes | 0 No |
Starting Time of LT & HT Motor
what is the difference between UPS & Inverter
why we are using Load factor?
what is the acceptable limit value for Desolve Gas Analysis/
Sir We have a REF relay connected to 10MVA(Y-Y) Transformer.on External earth fault REF relay trips along with earth fault relay.The REF relay has no complant as we tested relay.Why is it happening?
Dear sir, my knowledge about cable size determination is limited. Though I read examples I could not calculate the Cable size required for electric driven pump 40 KW, 380 Volt, 50 HZ, 50 meter from transformer and it is three phase star delta starting. Please help as there is no one in my surroundings to help.