We have a bank capacitor rating of 60 KVAR for a overall
load of 160 KVA and we have connected three loads of 50KVA
each. We would like to auto matically correct PF using APFC.
How do we design it?
Answers were Sorted based on User's Feedback
APFC panel should be connected to main incoming busbar i.e.
from where 160 kva load was fed. 60 kvar capacitors should
be devided into smaller capacities i.e you have to use
either 6x10 kvar or 4x 15kvar or 10x6kvar. I will consider
6x10 kvar. in APFC you have to programe each stage
capacity. here the value is 10 kavar. You have to take 6
no. of capcitor switching duty contactros and to be wired
as per the APFC. It also requires one CT signal and voltage
signal(any one of the three phases of main busbar). You can
program s/on and s/off time in APFC. and also you can
program target power factor. EPCOS apfc is the best
controller I have used.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / yuvraj gaikwad
devide the 60kvar capacitor into 4 or 6 banks of 15kvar or
10 kvar.use apfc relay of 4/6 stage which wil automatically
switch the cap banks to achive the target power factor.
The apfc i suggest is SYCON apfc which has more features
and available in diffrent models with fifo as well as
intelligent switching.visit website www.syconindia.com
| Is This Answer Correct ? | 3 Yes | 2 No |
What is C2-M2-E2 class in circuit breaker. why and where it is to be used in circuit breaker
What is floating voltage?
how to calculate IR value of 33KV cable ??
What is the difference between power,voltage,current? and with example
why use in & out Diesel line in dg set.
Why grounding is generally done in supply end?
why multiplying factor is used in wattmeter???
how to reduce power loss when the tranmission under long distance?
what is used root two in single phase line?
What is the ohms law?
In a 3 phase,400v,4 wire system, 2 incandescent lamps, one having 230v,100w and the other 230v,200w are connected between r phase- neutral and y phase-neutral respectively. If neutral wire breaks which lamp will fuse first and why?
how invertor convert the dc into ac give brif detail
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)