Answer / jitesh kotecha
induction motor is an inductive device and we know that in
inductive circuit current lags behind voltage due to the
inductive reactance of the motor. so that the phase angle
between voltage and current will increase. and the cosine
angle i.e. P.F. will decreases.to improve the p.f we have
to supply leading Kvar to the system. it is possible by
different way. either use capacitor bank which will supply
leading kvar to the syswtem and overall lagging kvar will
decreases and if we see the power triangle then the angle
between KW and KVA will decrease so that the p.f. will
improve. second method is to run synchronous motor on
leading p.f.in parallel with the system.
Is This Answer Correct ? | 34 Yes | 1 No |
Answer / karthikeyan
the above answer saying synchronous motor can be used but
we never see a synchronous installed near indution motor.
We always uses static capacitors to improve the overall PF.
why because only in High end generating stations and
substations the synchronous motor can be used to imrove
system PF. for medium and small loads we can go for static
capacitor bank.
Is This Answer Correct ? | 15 Yes | 1 No |
Answer / ravi
Bcoz the IM will drwa an Lagging Current..
We can use a APFC Bank to maintain it.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / umesh
induction motor have inductive materials which lags behand
the the voltage,that's way power factor decreases it
connected to induction motor,
PF can improve the power factor by connecting the
syncronous motor parralel to the incution motor ,
Syncronous motor running cost is costly, it will be run in
idle
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / aniket kumar
by decreasing the reactive power we can maintain the power factor to unity
Is This Answer Correct ? | 1 Yes | 2 No |
Answer / raushan singh
We can use capacitors to improve power factor in
Synchronous Alternators.
Is This Answer Correct ? | 4 Yes | 8 No |
How to take of Transformer oil Break down voltage test?
how to select cable size according to ampere.
In explosive and polluted environments which type of motors do we use?
what is the diff. btwn. electronic regulator and ordinary rheostat regulator for fans?
what is the difference between HV and LV Breakers?
4 Answers GM General Motors, OEG,
how to can we synchronize different capacity of DG sets.60kva& 250kva?
hw to find transformer is in normal position? whether its in charged condition or not? except humming sound?
how much distance is required for earth pit to earth pit in substation???
How do you calculate the actual power consumption of an inductive load appliance. Say, a deep freezer of 200watts
comparision between mcb,mccb,elcb,flcb,elcb in details
How many Zones can be in Conventional type fire alarm system & how can we detect the fire in Conv. type FAS?
what is suitable cable for 25 HP motor ? start with VFD ac supply 50 hz