Why P.f. of the system decreases when it is connectect
across induction motor? & how to maintain the p.f. of
system to unity.?
Answers were Sorted based on User's Feedback
Answer / jitesh kotecha
induction motor is an inductive device and we know that in
inductive circuit current lags behind voltage due to the
inductive reactance of the motor. so that the phase angle
between voltage and current will increase. and the cosine
angle i.e. P.F. will decreases.to improve the p.f we have
to supply leading Kvar to the system. it is possible by
different way. either use capacitor bank which will supply
leading kvar to the syswtem and overall lagging kvar will
decreases and if we see the power triangle then the angle
between KW and KVA will decrease so that the p.f. will
improve. second method is to run synchronous motor on
leading p.f.in parallel with the system.
Is This Answer Correct ? | 33 Yes | 1 No |
Answer / karthikeyan
the above answer saying synchronous motor can be used but
we never see a synchronous installed near indution motor.
We always uses static capacitors to improve the overall PF.
why because only in High end generating stations and
substations the synchronous motor can be used to imrove
system PF. for medium and small loads we can go for static
capacitor bank.
Is This Answer Correct ? | 15 Yes | 1 No |
Answer / ravi
Bcoz the IM will drwa an Lagging Current..
We can use a APFC Bank to maintain it.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / umesh
induction motor have inductive materials which lags behand
the the voltage,that's way power factor decreases it
connected to induction motor,
PF can improve the power factor by connecting the
syncronous motor parralel to the incution motor ,
Syncronous motor running cost is costly, it will be run in
idle
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / aniket kumar
by decreasing the reactive power we can maintain the power factor to unity
Is This Answer Correct ? | 1 Yes | 2 No |
Answer / raushan singh
We can use capacitors to improve power factor in
Synchronous Alternators.
Is This Answer Correct ? | 4 Yes | 8 No |
Efficient electrical earthing in hard rock area
what is the difference between high impedance REF & REF, same high impedance differential protection & differential protection for Power transformer?
Difference between single phase rotary inverter and 3 phase rotary inverter
WHAT is the no of starts/hr for 3.3 KV, 300 KW motor. Motor is vertical flange type.
why the conservater tank alwes made upper side of transformer???
Why resistance is not measure in running conditions of motor
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
how to calculate voltage drop and followed by cable calculation?is there avail in formula?
How do you maintain the earthing resistance?
13 Answers Birla, Ford, JLL,
WHAT IS RMU & HOW IT WORK,IT USEFUL FOR HT OT LT POWER DISTRIBUTION MAUFACTUERE IN INDIA.
What are the difference between off-load tap changer and on-load tap changer in transformer?
how power saving takes place through VFD?